Steve,

I have been doing sprinkler design for over 50years and our NZ
Standard/Rules have been based on FOC/UK rules for most of that time. Only
in recent years have we adopted FM/NFPA for some of our Extra High Hazard.

Hence I think of Mains (usually 65 - 200+mm nominal bore) as feed pipes and
Ranges (usually 25 - 50mm  nb) as pipes which have sprinklers attached
either directly or by droppers/risers. Of course Storage/ESFR sprinklers
have now made us use 65 and 80mm nb pipes with sprinklers directly attached.

 

Cheers,

Russell Gregory

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Friday, 28 October 2016 6:13 AM
To: [email protected]
Subject: RE: Hydraulic losses when using a Mechanical Tee on Sprinkler
Outlet

 

Russell:

 

What does the term "range pipe" refer to?

 

 

Steve Leyton 

 

 

-------- Original message --------

From: Russell & Carol Gregory <[email protected]> 

Date: 10/27/16 1:31 AM (GMT-08:00) 

To: [email protected] 

Subject: Hydraulic losses when using a Mechanical Tee on Sprinkler Outlet 

 

I posted a message on this subject early this month but only received one
reply(thanks Brad). This was surprising as I thought it was a serious
problem if the full EQL for tee had to be added to calculations. Especially
if the change was made on-site after design had been completed with welded
outlets.

So my query is as follows;

 

When calculating a Range Pipe with welded threaded outlets for sprinklers it
is not necessary to include a loss for the water leaving the range pipe and
entering the sprinkler. The total pressure is assumed to apply to the
sprinkler orfice.

This means that a 80nb pipe with a 25nb outlet and a k36 sprinkler does not
have an additional loss added for the outlet fitting.

 

If I change my design and fabricate the 80nb range pipe with 80 x 25
Mechanical Tees for the Sprinkler outlet do I have to apply an additional
loss factor for that fitting? The published EQL for Mech tees varies greatly
between brands,( 0.8m up to 2.4m). This means a head pressure of 345kPa
would need around 600kPa in the range if this additional loss is added.

 

Questions;

1.       Is it common practice in USA to use 80 x 25 clamp/mechanical tees
for attaching large bore Storage Sprinklers directly to 80nb range pipes?

2.       Is it common practice to add in an additional loss for the clamp
tee, in the hydraulic calculation, where the sprinkler is directly fitted to
the tee outlet?  

 

I would appreciate the Forum members advise as to what is the standard
practice in the USA.

 

Russell Gregory

Christchurch 

New Zealand

 

e-mail [email protected]

 