Must confess that I have not reviewed the cut-sheet but ASSUME that it 
addresses this issue. 

Also note that extensions up to 2 inch is not required to be added to the 
calculation.  Have not looked to see if any longer than 2 inch exist (since it 
is required to be listed).  Also use of a longer extension will be a kick in 
the hydraulic head since now the tee must also be included in the calc.  Any 
guesses if Mr Truck Slammer would include it?

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>



> On Oct 27, 2016, at 8:08 AM, Todd Williams <[email protected]> wrote:
> 
> Ken,
> 
> I brought that up because in NFPA 13, they are called "flexible fittings" not 
> "flexible drops". My thinking is that FUBAR Fire Protection (or someone like 
> them) is going to try to claim the since NFPA call them fittings that they 
> won't have to include them in the calcs. 
> 
> Todd G Williams, PE