We have an newly constructed open parking garage with a surrounding skywalk. 
The building official is now asking for fire barriers complying with Chapter 31 
between the two and the owner and architect want to deal with this using the 
exception that uses fire protection sprinklers for equivalency. It appears to 
me that the Code is asking us to protect the parking garage from the skywalk as 
the Code says to install fire protection sprinklers on the "interior" of the 
wall (which is the garage side) that fully wet the wall as a compliance path. 
We already have a fully sprinklered structure, with a row of dry sprinklers 
eight feet and eight feet on center away on the garage side, but the published 
spray pattern for the Reliable F1FR56 upright installed by the contractor would 
leave the top 3 feet of the wall unwetted.

It appears to me I would have to install an additional row of heads right along 
the wall, but even then, it looks like the spray pattern shows drop off at any 
sort of reasonable spacing so some parts of the wall remain unwetted.  What 
have others done in this situation?