I’m surprized no one participating in this thread has mentioned NFPA 45 or its 
extracted text in Section 22.8 of NFPA 13-2016.

If there are chemicals used in the lab in question, the amount needs to be 
determined to enable classification of the space as a Class A, B, C or D type 
lab. Then Class A or B are designated as OH2 occupancies and Class C or D are 
considered OH1.

If there are no chemicals, then you could classify the lab occupancy based on 
the Occupancy definitions.

Larry Keeping

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: December-05-16 10:55 AM
To: sprinklerforum <[email protected]>
Subject: Re: College Lab Classrooms

Surely you jest.

________________________________
From: "Brad Casterline" 
<[email protected]<mailto:[email protected]>>
To: "sprinklerforum" 
<[email protected]<mailto:[email protected]>>
Sent: Monday, December 5, 2016 10:47:57 AM
Subject: RE: College Lab Classrooms

that's easy to answer!
From NFPA 13 (most editions for years):

5.2* Light Hazard Occupancies. Light hazard occupancies shall
be defined as occupancies or portions of other occupancies
where the quantity and/or combustibility of contents is low and
fires with relatively low rates of heat release are expected.
5.3* Ordinary Hazard Occupancies.
5.3.1* Ordinary Hazard (Group 1).
5.3.1.1 Ordinary hazard (Group 1) occupancies shall be defined
as occupancies or portions of other occupancies where
combustibility is low, quantity of combustibles is moderate,
stockpiles of combustibles do not exceed 8 ft (2.4 m), and fires
with moderate rates of heat release are expected.
5.3.1.2 Dedicated and miscellaneous storage shall be protected
in accordance with Chapter 12 and Chapter 13 as applicable.
5.3.2* Ordinary Hazard (Group 2).
5.3.2.1 Ordinary hazard (Group 2) occupancies shall be defined
as occupancies or portions of other occupancies where the
quantity and combustibility of contents are moderate to high,
stockpiles of contents with moderate rates of heat release do not
exceed 12 ft (3.66 m), and stockpiles of contents with high rates
of heat release do not exceed 8 ft (2.4 m).
5.3.2.2 Dedicated and miscellaneous storage shall be protected
in accordance with Chapter 12 and Chapter 13 as applicable.

________________________________
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]<mailto:[email protected]>
Sent: Monday, December 05, 2016 9:36 AM
To: sprinklerforum
Subject: College Lab Classrooms

Quick question.
College Lab classrooms.  Light or Ordinary hazard?


Bill Menster
WFM Consulting Inc.
2416 Malaya Ct.
Punta Gorda, FL 33983
ph. 941-421-9786
fax 941-391-6133
[email protected]<mailto:[email protected]>
www.wfmconsultinginc.com<http://www.wfmconsultinginc.com>


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to