Mike,
    there's some explanatory text in the handbook.

   A recessed escutcheon is part of a listed sprinkler assembly, and
   therefore, it should be attached tothe sprinkler as intended by the
   sprinkler manufacturer and not require glue or caulk for attachment.
Theapplication of glue or caulk could interfere with the intended operation by blocking vent holes or clearancesbetween moving parts.

I knew the text of the section, however I had not read the additional information from the handbook.
sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 12/14/2016 1:29 PM, Mike B Morey wrote:
NFPA 13 2013:
6.2.7.4 The use of caulking or glue to seal the penetration or to affix the components of a recessed escutcheon or concealed cover plate shall not be permitted.


------------------------------------------------------------------------

*/Mike Morey/*
*Project Manager* • Fire Protection*
Shambaugh & Son, LP */an EMCOR Company/
7614 Opportunity Drive • Fort Wayne, IN • 46825
*direct *260.487.7824*/  cell *260.417.0625*/  fax *260.487.7991*
email *mmo...@shambaugh.com







From: Matt Grise <m...@afpsprink.com>
To: "sprinklerforum@lists.firesprinkler.org" <sprinklerforum@lists.firesprinkler.org>
Date: 12/14/2016 04:24 PM
Subject: sealing sprinkler head penetrations
Sent by: "Sprinklerforum" <sprinklerforum-boun...@lists.firesprinkler.org>
------------------------------------------------------------------------



We are working on a single story residential project where the piping is run in the attic to supply semi-recessed pendants in the dwelling space. The GC is working on an Energy Star rating and is going to do a fan test to determine how tight the building envelope is. They would like us to seal around the outer trim ring so that no air can get through during the fan test. The GC suggested that we apply a bead of clear silicone caulk around the outside of the trim ring to do that.

We are pushing back against using a generic sealant on the escutcheons, but as long as it does not get on the sprinkler I can’t really think of any code issue.

Has anyone heard of a situation like this (outside of a clean room)?

Thanks!

Matt Grisé
*/Alliance Fire Protection/*
130 w 9th Ave.
North Kansas City, MO 64116
/
*Licensed in KS & MO/

913.888.0647 ph
913.888.0618 f
913.526.7443 cell_
__www. AFPsprink.com_ <www.%20AFPsprink.com>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DgICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=rWRu1NiE4d4HqERsxYp6NHnUKc2eQBFeQlj9GDU24rs&s=IEecWiVaYpA-MybXk2r1rE0HJ6m5HbLjVcDjpldEmlY&e=

This message is for the named person's use only. It may contain confidential, proprietary or legally privileged information. No confidentiality or privilege is waived or lost by any mistransmission. If you receive this message in error, please immediately delete it and all copies of it from your system, destroy any hard copies of it and notify the sender. You must not, directly or indirectly, use, disclose, distribute, print, or copy any part of this message if you are not the intended recipient.


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to