Matt,

I was on a project in my field days where the building was tested for to LEED 
requirements for air leakage. We used extended escutcheons and the GC caulked 
around the pipe protruding from the wall. I know of a couple units that failed 
the air leakage test because there was not enough caulk around the pipe at the 
drywall. That being the case, I imagine it would fail horribly without the 
penetration(s) being sealed.

TAYLOR SCHUMACHER, CET
Security Fire Sprinkler
P  320.656.0847  |  F  320.656.0312  |  E  tay...@sfsprinkler.com

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Parsley Consulting
Sent: Wednesday, December 14, 2016 4:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: sealing sprinkler head penetrations

Matt,
    I'm not aware of those evaluations, I've never done one, and never had to 
interpret one, so in that respect I'm quite unqualified.
    However, I know, as you do, that the standard governing the installation of 
a sprinkler system tells me specifically not to do that, and doesn't provide a 
word of guidance on how such testing should be evaluated.  Stepping outside of 
that limitation is something I'm very careful to avoid.
    Lacking any information on that sort of issue, I'll let the contractor 
pushing for the use of caulking know that lacking any guidance from a 
conflicting standard or code, I'll follow NFPA 13 and refuse to do what he's 
asking.
sincerely,
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit our website<http://www.parsleyconsulting.com/>
On 12/14/2016 2:16 PM, Matt Grise wrote:
I have no idea if it will pass or not. I am not familiar with the requirements.

Anyone out there know how much a sprinkler head or two per room affects this 
sort of testing?

Matt Grisé PE*, LEED AP, NICET II
Vice President - New Construction
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.526.7443 cell
www. AFPsprink.com


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brad Casterline
Sent: Wednesday, December 14, 2016 4:15 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: sealing sprinkler head penetrations


So at this point they can do the fan test w/o sealed escutcheons-- it might 
pass anyway!

How tight does it have to be to get a gold star?

...

Residential Sprinkler Systems Always Save Lives

Brad
On Dec 14, 2016 4:02 PM, "Matt Grise" 
<m...@afpsprink.com<mailto:m...@afpsprink.com>> wrote:
Thanks! This AHJ is working with 2010 edition, so I had not seen that section - 
sounds like a pretty clear intent to address though.

Matt Grisé


From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Parsley Consulting
Sent: Wednesday, December 14, 2016 3:46 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: sealing sprinkler head penetrations

Mike,
    there's some explanatory text in the handbook.
A recessed escutcheon is part of a listed sprinkler assembly, and therefore, it 
should be attached to the sprinkler as intended by the sprinkler manufacturer 
and not require glue or caulk for attachment. The application of glue or caulk 
could interfere with the intended  operation by blocking vent holes or 
clearances between moving parts.
    I knew the text of the section, however I had not read the additional 
information from the handbook.
sincerely,
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181<tel:%28760%29%20745-6181>
Visit our website<http://www.parsleyconsulting.com/>
On 12/14/2016 1:29 PM, Mike B Morey wrote:
NFPA 13 2013:
6.2.7.4 The use of caulking or glue to seal the penetration or to affix the 
components of a recessed escutcheon or concealed cover plate shall not be 
permitted.
________________________________

Mike Morey
Project Manager * Fire Protection
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824<tel:%28260%29%20487-7824> /  cell 
260.417.0625<tel:%28260%29%20417-0625> /  fax 
260.487.7991<tel:%28260%29%20487-7991>
email mmo...@shambaugh.com<mailto:mmo...@shambaugh.com>

[cid:image001.jpg@01D25629.78EC84E0]





From:        Matt Grise <m...@afpsprink.com><mailto:m...@afpsprink.com>
To:        
"sprinklerforum@lists.firesprinkler.org"<mailto:sprinklerforum@lists.firesprinkler.org>
 
<sprinklerforum@lists.firesprinkler.org><mailto:sprinklerforum@lists.firesprinkler.org>
Date:        12/14/2016 04:24 PM
Subject:        sealing sprinkler head penetrations
Sent by:        "Sprinklerforum" 
<sprinklerforum-boun...@lists.firesprinkler.org><mailto:sprinklerforum-boun...@lists.firesprinkler.org>
________________________________



We are working on a single story residential project where the piping is run in 
the attic to supply semi-recessed pendants in the dwelling space. The GC is 
working on an Energy Star rating and is going to do a fan test to determine how 
tight the building envelope is. They would like us to seal around the outer 
trim ring so that no air can get through during the fan test. The GC suggested 
that we apply a bead of clear silicone caulk around the outside of the trim 
ring to do that.

We are pushing back against using a generic sealant on the escutcheons, but as 
long as it does not get on the sprinkler I can't really think of any code issue.

Has anyone heard of a situation like this (outside of a clean room)?

Thanks!

Matt Grisé
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO

913.888.0647<tel:%28913%29%20888-0647> ph
913.888.0618<tel:%28913%29%20888-0618> f
913.526.7443<tel:%28913%29%20526-7443> cell
www. AFPsprink.com<http://www.%20AFPsprink.com>
 _______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DgICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=rWRu1NiE4d4HqERsxYp6NHnUKc2eQBFeQlj9GDU24rs&s=IEecWiVaYpA-MybXk2r1rE0HJ6m5HbLjVcDjpldEmlY&e=
This message is for the named person's use only. It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission. If you receive this message in error, 
please immediately delete it and all copies of it from your system, destroy any 
hard copies of it and notify the sender. You must not, directly or indirectly, 
use, disclose, distribute, print, or copy any part of this message if you are 
not the intended recipient.




_______________________________________________

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




_______________________________________________

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>