My understanding of backflow performance and the mapping of those curves is 
that the devices impose more pressure loss at opening than at closing. So that 
spike at 0 GPM is an accurate reflection of the higher pressure loss that 
occurs at the initiation of a flow event and it almost always ramps right back 
down once flow rate gets into the dozens or above 100.

But at zero flow, we've always used the ambient static and my vague 
recollection is that several years ago I confirmed this either with our local 
Wilkins rep are their factory in San Luis Obispo. I do know that we have never 
been corrected by an AHJ or third party consultant so I'm 99.9% sure that this 
is the accepted best practice.


Steve L.



-------- Original message --------
From: Dewayne Martinez <[email protected]>
Date: 1/11/17 5:41 AM (GMT-08:00)
To: [email protected]
Subject: Static pressure after backflow preventer

Is there really a pressure loss at 0gpm flow for backflow preventers like the 
curves show?  I am trying to figure out my static pressure on a floor level 
with a fire pump at churn and it needs to be accurate.
Thanks,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[cid:[email protected]] [cid:[email protected]]  
[cid:[email protected]]  [Top Workplaces 2015]

TOTAL Mechanical voted "Top Workplace" for a 4th consecutive year.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to