I'm flying by the seat of my pants (with no lights) but until I prove to myself 
otherwise (or am beat into submission by the technical committee), I don’t see 
why we should beat ourselves up and default to what ever seems to be the most 
conservative.  Our supply curve is a straight line relationship from static to 
some lower residual pressure.  We now incorporate a device that has a crazy 
high initial pressure loss that then drops back into a more normal curve.  In 
looking at SYSTEM DEMAND are we well served by ignoring the actual available 
pressure that was otherwise lost due to accounting for a wiggle at the front 
end.

 For now, I’ll stick with my mantra:  Lead the way, Mr. Custer. I’m right 
behind you.


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Jan 11, 2017, at 12:27 PM, Dewayne Martinez 
> <[email protected]> wrote:
> 
> I have used the static without the backflow loss in the past but I noticed 
> with the SprinkCad software I am running it uses the mfg curves and it was 
> showing less static than I had figured.  If I take into account the BFP loss 
> I can eliminate 6 pressure reducing hose valves…..Looks like I will err on 
> the side of caution and design them in.
> Thanks,
> Dewayne
>  