It ha's been my understanding that a structual engineer designs a hanger it 
separates any responsibility from the sprinkler contractor.

Begat they are a pre with more knowledge in the specific area.

Thought there was a blurb in NFPA 13 along those lines

Sent from my Verizon 4G LTE Droid
On Jan 12, 2017 5:01 PM, Jerry Van Kolken <[email protected]> wrote:
I have a project where we are having a structural eng. design some pipe support 
for us. In 9.1.1.2 (3) it says the supports still need to be spaced per table 
9.2.2.1(a).

If I have piping larger than 8” and the engineer approves it would be 
acceptable to space supports over 15’-0”?

Jerry Van Kolken