Your welcome...:) I will get that arrangement approved with the contractor on 
Monday. The fix should keep the trainee busy for a day or two, lol


John Paulsen 

Crown Fire System Design 




Get Outlook for Android









On Sun, Jan 29, 2017 at 4:07 PM -0500, "Brad Casterline" 
<[email protected]> wrote:












Centered on the partial height partitions sounds perfect, and with a little 
creative staggered spacing you could avoid baffles.


Odds are your AHJ would concur.


You're welcome and thank you for my weekend sprinkler puzzle ;)


Brad
On Jan 29, 2017 1:16 PM,  <[email protected]> wrote:


Thanks guys for your comments. I feel like I am trying to choose between evils 
here. If I can't place the sprinkler over the top of the low partition to spray 
on both sides, I am definitely going to cold shower on the 5' & 7' wide 
units....this project just became 4 stories of real problems.


Thanks,

John Paulsen 

Crown Fire System Design 




Get Outlook for Android









On Sun, Jan 29, 2017 at 1:29 PM -0500, "Pete Schwab" <[email protected]> 
wrote:












There have been submittals to SSI to allow the partition rule for OH. They have 
been rejected since no one has submitted testing data. So in response to the 
original question, yes you have to consider each partition as it went to the 
ceiling and yes you still have to be concerned with cold soldering. Many of the 
national self-storage facility owners/builders understand that the top of 
storage must be 18” from the sprinkler deflector (Usually accomplished with 
chicken wire) .

 

Pete Schwab

 

My opinion only and not that of the NFPA or any of its committees

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Sunday, January 29, 2017 12:59 PM
To: [email protected]
Subject: RE: Floor mounted obstructions - ORDINARY HAZ

 

John,

I agree with your 'common sense' statement, so this has been bothering me since 
you posted it.

I'm looking at NFPA 13 (2013), Fig. 8.6.5.2.2, and imagining my cubicle at the 
office. "A"=~36" and "B"=~30". The next sprinkler to the right is about 11' 
from the partition.
My space is to the right side, and I have a kind of narrow counter against the 
partion with papers and prints scattered across it.
Now I imagine the sprink shown in the fig activating, and 20-30% of the pattern 
being thrown over the partition and landing on the floor a few feet beyond the 
counter.
Maybe The Committee felt that type of thing would be acceptable for LH but not 
OH?

Brad

On Jan 28, 2017 11:39 AM, "John Paulsen" <[email protected]> wrote:

Jeff:

 

Amen on the “not clearly stated”!  I saw that paragraph, but it appeared to me 
to refer more to obstructions from the ceiling not the floor. I’m trying to 
throw over the top of the partition and it would be nice if NFPA-13 could give 
a spacing table for Ordinary Hazard like it does for “Light Hazard only”. 
That’s the frustrating part, common sense says the same or similar spacing 
would apply, but Ordinary Hazard is not included.

 

Thanks,

 

John Paulsen – SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P – 614-782-2438

F – 614-782-2374

C – 614-348-8206

 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jeff Normand
Sent: Saturday, January 28, 2017 12:32 PM
To: [email protected]
Subject: Re: Floor mounted obstructions - ORDINARY HAZ

 

Not that clearly stated but here's the NFPA 13 2016 edition

 

 

8.6.5.3.1 Continuous or noncontinuous obstructions that interrupt

the water discharge in a horizontal plane more than

18 in. (450 mm) below the sprinkler deflector in a manner to

limit the distribution from reaching the protected hazard

shall comply with 8.6.5.3.

 

8.6.5.3.2 The requirements of 8.6.5.3 shall also apply to obstructions

18 in. (450 mm) or less below the sprinkler for light

and ordinary hazard occupancies.

 

A.8.6.5.3.3 When obstructions are located more than 18 in.

(450 mm) below the sprinkler deflector, an adequate spray

pattern develops and obstructions up to and including 4 ft

(1.2 m) wide do not require additional protection underneath.

Examples are ducts, decks, open grate flooring, catwalks,

cutting tables, overhead doors, soffits, ceiling panels,

and other similar obstructions.

 

On Sat, Jan 28, 2017 at 11:10 AM, John Paulsen <[email protected]> wrote:

I am trying to determine the proper deflector distance from a partition with 
the top located 18” below the sprinkler deflector. This is an Ord Haz Grp II 
Self Storage facility with standard spray QR Tyco TY-FRB TY3131 uprights. Sec 
8.6.5.2 doesn’t give a table like 8.6.5.2.2 which is for Light Hazard only. 

 

If I have to space the heads as if the low partitions went all the way to the 
deck, I will violate the 6’ minimum rule. What am I missing here?   

 

Thanks,

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org








_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to