NFPA 13, 2013
11.1.2* Adjacent Hazards or Design Methods. For buildings with two or more 
adjacent hazards or design methods, the following shall apply:
(1) Where areas are not physically separated by a barrier or partition capable 
of delaying heat from a fire in one area from fusing sprinklers in the adjacent 
area, the required
sprinkler protection for the more demanding design basis shall extend 15 ft 
(4.6 m) beyond its perimeter.





Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tim Easter
Sent: Thursday, March 02, 2017 8:58 AM
To: 
[email protected]<mailto:[email protected]>
Subject: different k-factors in same area [EXTERNAL]

I have a half-wall that separates an office area from a warehouse area. The 
design is for K factors of 8.0 inside warehouse area, and 5.6 inside office 
area. But since the halfwall doesn't reach the deck the area above the office 
area protected from the ceiling  must have same k-factor as warehouse correct? 
Can anyone point that out in NFPA 13 as a code reference?



Tim Easter, PE
[Description: Description: Description: 
http://www.wwgfp.com/MailLogo.gif]<http://www.wwgfp.com/Brochere.jpg>
522 Stockton Street
Jacksonville, FL 32204
Office: (904) 387-7973  Cell: (904) 476-4325  Fax: (904) 394-7261





     This electronic message contains information from W. W. Gay Fire 
Protection, Inc., which may be confidential or privileged. The information is 
for use of the individual or the entity named above. If you are not the 
intended recipient, please be aware that any disclosure, copying, distribution 
or use of the contents of this message is prohibited. If you have received this 
electronic transmission in error, please notify us immediately at 
1-904-387-7973.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to