Does the ½” outlet provided by removing the sprinkler not satisfy this? Unless you have some more trapping?
R/ Matt Matthew J. Willis Project Manager Rapid Fire Protection Inc.<http://rapidfireinc.com/> 1530 Samco Road Rapid City, SD 57702 Office-605.348.2342 Direct Line-605.593.5063 Cell-605.391.2733 Fax:-605.348.0108 [cid:[email protected]] From: Sprinklerforum [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Friday, March 3, 2017 11:50 AM To: [email protected] Subject: Dry system return bend - aux drain needed? NFPA 13 (07ed) Section 8.16.2.5.3.3 states that aux drains are not required for pipe drops supplying dry-pendant sprinklers installed per 7.2.2 7.2.2 address both listed dry type sprinklers and pendant sprinklers installed on a return bend in a heated space I have someone questioning if aux drains are required for pendant sprinklers on return bends because they not specifically “dry-pendant”. I have always figured that if they were in section 7.2.2 then no aux drain would be needed. What say’s the forum on this? Thanks, Dewayne