Does the ½” outlet provided by removing the sprinkler not satisfy this?

Unless you have some more trapping?

R/
Matt

Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:[email protected]]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Friday, March 3, 2017 11:50 AM
To: [email protected]
Subject: Dry system return bend - aux drain needed?

NFPA 13 (07ed)

Section 8.16.2.5.3.3 states that aux drains are not required for pipe drops 
supplying dry-pendant sprinklers installed per 7.2.2
7.2.2 address both listed dry type sprinklers and pendant sprinklers installed 
on a return bend in a heated space

I have someone questioning if aux drains are required for pendant sprinklers on 
return bends because they not specifically “dry-pendant”.  I have always 
figured that if they were in section 7.2.2 then no aux drain would be needed.  
What say’s the forum on this?
Thanks,

Dewayne