What a horrible waste of time. Hopefully this wasnt your local government inspector asking this. If so, you should call the mayor and ask to be reimbursed. Of course you dont need a drain on every sprinkler.
On Fri, Mar 3, 2017 at 1:49 PM, Dewayne Martinez < dmarti...@total-mechanical.com> wrote: > NFPA 13 (07ed) > > > > Section 8.16.2.5.3.3 states that aux drains are not required for pipe > drops supplying dry-pendant sprinklers installed per 7.2.2 > > 7.2.2 address both listed dry type sprinklers and pendant sprinklers > installed on a return bend in a heated space > > > > I have someone questioning if aux drains are required for pendant > sprinklers on return bends because they not specifically “dry-pendant”. I > have always figured that if they were in section 7.2.2 then no aux drain > would be needed. What say’s the forum on this? > > Thanks, > > > > Dewayne > > > > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >