What a horrible waste of time. Hopefully this wasnt your local government
inspector asking this. If so, you should call the mayor and ask to be
reimbursed. Of course you dont need a drain on every sprinkler.

On Fri, Mar 3, 2017 at 1:49 PM, Dewayne Martinez <
dmarti...@total-mechanical.com> wrote:

> NFPA 13 (07ed)
>
>
>
> Section 8.16.2.5.3.3 states that aux drains are not required for pipe
> drops supplying dry-pendant sprinklers installed per 7.2.2
>
> 7.2.2 address both listed dry type sprinklers and pendant sprinklers
> installed on a return bend in a heated space
>
>
>
> I have someone questioning if aux drains are required for pendant
> sprinklers on return bends because they not specifically “dry-pendant”.  I
> have always figured that if they were in section 7.2.2 then no aux drain
> would be needed.  What say’s the forum on this?
>
> Thanks,
>
>
>
> Dewayne
>
>
>