NFPA 13D, 2017 (the edition currently in force in PA) 8.2.5.6.3 Where sidewall sprinklers are more than 3 ft. above the top of cabinets, the sprinkler shall be permitted to be installed on the wall above the cabinets where the cabinets are no greater than 12 in. from the wall.
We have a case that meets all of the above criteria except for a 2" wide crown molding around the top of the cabinets, so the overall width is 14" around the top of the cabinet. Obvious solution is put the sprinkler on the other end of the room, however that wall is a rated wall with a un-conditioned space on the other side. Any sugestions? Richard Mote Design Manager [http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg] P: 570.837.7647 * W: 877.324.ROWE * F: 570.837.6335 PO Box 407 * 7993 US Route 522, Suite 1 * Middleburg, PA 17842 RoweSprinkler.com * [email protected]<mailto:[email protected]> *** Confidentiality Notice *** This email and any attachments thereto may contain information that is privileged and confidential and is intended only for the use of the addressee. If the reader of the message is not the intended recipient or an authorized representative of the intended recipient, you are hereby notified that any dissemination of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by e-mail at [email protected] or by telephone at 570-837-7647 and delete the message and any attachments permanently from your system.