NFPA 13D, 2017 (the edition currently in force in PA) 8.2.5.6.3 Where sidewall 
sprinklers are more than 3 ft. above the top of cabinets, the sprinkler shall 
be permitted to be installed on the wall above the cabinets where the cabinets 
are no greater than 12 in. from the wall.

We have a case that meets all of the above criteria except for a 2" wide crown 
molding around the top of the cabinets, so the overall width is 14" around the 
top of the cabinet. Obvious solution is put the sprinkler on the other end of 
the room, however that wall is a rated wall with a un-conditioned space on the 
other side.
Any sugestions?


Richard Mote
Design Manager
[http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg]
P: 570.837.7647  *  W: 877.324.ROWE  *  F: 570.837.6335
PO Box 407 * 7993 US Route 522, Suite 1 * Middleburg, PA 17842
RoweSprinkler.com  *  
[email protected]<mailto:[email protected]>

*** Confidentiality Notice ***
This email and any attachments thereto may contain information that is 
privileged and confidential and is intended only for the use of the addressee. 
If the reader of the message is not the intended recipient or an authorized 
representative of the intended recipient, you are hereby notified that any 
dissemination of this communication is strictly prohibited. If you have 
received this communication in error, please notify us immediately by e-mail at 
[email protected] or by telephone at 570-837-7647 and delete the 
message and any attachments permanently from your system.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to