Sloped ceiling?   Can a sidewall be oriented so it discharges down-slope?

You comment sent me scurrying to our tech data library and also to NFPA 13D and 
13.  Both standards are mute regarding the positioning of residential 
horizontal sidewall sprinklers on/under sloped ceilings.   Viking tech data 
sheets say to refer to the appropriate standard.  Tyco says their RHSW 
sprinklers can be used under sloped ceilings but no specific positioning 
criteria is offered.   If we use the spray sprinkler criteria, the sprinklers 
have to be oriented so they are placed at the peak of a sloped ceiling and 
spray downward.

Am I missing something somewhere regarding RHSW sprinklers and sloped ceilings?

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote
Sent: Tuesday, March 07, 2017 6:18 AM
To: [email protected]
Subject: RE: Cabinets Against a Wall

This a sloped ceiling area, with the ceiling being attached directly to the 
underside of the joists. No space to run pendants in a conditioned area.

Richard Mote
Design Manager
[http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg]
P: 570.837.7647  *  W: 877.324.ROWE  *  F: 570.837.6335
PO Box 407 * 7993 US Route 522, Suite 1 * Middleburg, PA 17842
RoweSprinkler.com  *  
[email protected]<mailto:[email protected]>

*** Confidentiality Notice ***
This email and any attachments thereto may contain information that is 
privileged and confidential and is intended only for the use of the addressee. 
If the reader of the message is not the intended recipient or an authorized 
representative of the intended recipient, you are hereby notified that any 
dissemination of this communication is strictly prohibited. If you have 
received this communication in error, please notify us immediately by e-mail at 
[email protected]<mailto:[email protected]> or by telephone at 
570-837-7647 and delete the message and any attachments permanently from your 
system.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Tuesday, March 07, 2017 8:56 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Cabinets Against a Wall

Pendant sprinkler?

Matt


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote
Sent: Tuesday, March 07, 2017 7:50 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Cabinets Against a Wall

NFPA 13D, 2017 (the edition currently in force in PA) 8.2.5.6.3 Where sidewall 
sprinklers are more than 3 ft. above the top of cabinets, the sprinkler shall 
be permitted to be installed on the wall above the cabinets where the cabinets 
are no greater than 12 in. from the wall.

We have a case that meets all of the above criteria except for a 2" wide crown 
molding around the top of the cabinets, so the overall width is 14" around the 
top of the cabinet. Obvious solution is put the sprinkler on the other end of 
the room, however that wall is a rated wall with a un-conditioned space on the 
other side.
Any sugestions?


Richard Mote
Design Manager
[http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg]
P: 570.837.7647  *  W: 877.324.ROWE  *  F: 570.837.6335
PO Box 407 * 7993 US Route 522, Suite 1 * Middleburg, PA 17842
RoweSprinkler.com  *  
[email protected]<mailto:[email protected]>

*** Confidentiality Notice ***
This email and any attachments thereto may contain information that is 
privileged and confidential and is intended only for the use of the addressee. 
If the reader of the message is not the intended recipient or an authorized 
representative of the intended recipient, you are hereby notified that any 
dissemination of this communication is strictly prohibited. If you have 
received this communication in error, please notify us immediately by e-mail at 
[email protected]<mailto:[email protected]> or by telephone at 
570-837-7647 and delete the message and any attachments permanently from your 
system.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to