My read on this would be that if you gave a sprinkler in the middle of a
24" horizontal duct you have 12" on center. Don't you need one at the top
of each vertical run?
On Thu, Mar 16, 2017 at 1:47 PM James Crawford <jcrawf...@phaserfire.ca>
wrote:

> NFPA #33 (2016 ed) section 9.4.6 (2) Horizontal Exhaust ducts shall have
> sprinklers located on 12’-0” centers beginning no more that 6’-0” from the
> duct entrance.
>
>
>
> If the horizontal run is only 2’-0” do you require a sprinkler head to
> protect this section of the duct, (is there a minimum distance)
>
>
>
>
>
> Thank you
>
>
>
>
>