Is that the total duct length or is there a riser to the roof?

Are there heads in the plenum behind the filter?

Where is the exhaust  fan?

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Thursday, March 16, 2017 4:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Paint Booth Exhaust Stack

 

NFPA #33 (2016 ed) section 9.4.6 (2) Horizontal Exhaust ducts shall have
sprinklers located on 12'-0" centers beginning no more that 6'-0" from the
duct entrance.

 

If the horizontal run is only 2'-0" do you require a sprinkler head to
protect this section of the duct, (is there a minimum distance)

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus