Do you have the resources to scan/send that section of the FBC? I’m not aware of any amendments in states’ building code adoptions that would create defacto high-rise standpipe requirements for non-high-rise buildings. I’m aware of at least two city ordinances that do, both out West and both municipal only. I’d like to see that language so send to me off-forum if you can please.
Pete Schwab – is this correct? Steve L. From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, March 23, 2017 8:20 AM To: sprinklerforum Subject: OBC, FBC, IBC / Standpipe Requirements My experience has been mainly in Ohio and Florida. Over the years, it seems the standpipe requirements have been constantly changing and confusing regarding the pressure requirements (100psi, 65 psi, etc.) and the allowance of 'Manual' standpipes. Here in Florida, the latest FBC has dropped the exception to allow manual wet standpipe in fully sprinklered buildings less than 75' in height. The current OBC also does not allow this exception. I assume this is due to the adoption of IBC. This means that almost every building that requires a standpipe, will also require a fire pump. In asking around, it seems that many people in the industry and AHJ's are either unaware of or ignore this. My question is, what is your experience / understanding of this? Thanks Bill Menster WFM Consulting Inc. 2416 Malaya Ct. Punta Gorda, FL 33983 ph. 941-421-9786 fax 941-391-6133 [email protected]<mailto:[email protected]> www.wfmconsultinginc.com<http://www.wfmconsultinginc.com>