Do you have the resources to scan/send that section of the FBC?   I’m not aware 
of any amendments in states’ building code adoptions that would create defacto 
high-rise standpipe requirements for non-high-rise buildings.  I’m aware of at 
least two city ordinances that do, both out West and both municipal only.   I’d 
like to see that language so send to me off-forum if you can please.

Pete Schwab – is this correct?

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Thursday, March 23, 2017 8:20 AM
To: sprinklerforum
Subject: OBC, FBC, IBC / Standpipe Requirements

My experience has been mainly in Ohio and Florida.  Over the years, it seems 
the standpipe requirements have been constantly changing and confusing 
regarding the pressure requirements (100psi, 65 psi, etc.) and the allowance of 
'Manual' standpipes.  Here in Florida, the latest FBC has dropped the exception 
to allow manual wet standpipe in fully sprinklered buildings less than 75' in 
height.  The current OBC also does not allow this exception. I assume this is 
due to the adoption of IBC.

This means that almost every building that requires a standpipe, will also 
require a fire pump.

In asking around, it seems that many people in the industry and AHJ's are 
either unaware of or ignore this.

My question is, what is your experience / understanding of this?
Thanks

Bill Menster
WFM Consulting Inc.
2416 Malaya Ct.
Punta Gorda, FL 33983
ph. 941-421-9786
fax 941-391-6133
[email protected]<mailto:[email protected]>
www.wfmconsultinginc.com<http://www.wfmconsultinginc.com>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to