Ohio Building Code refers to NFPA. Manual standpipes are OK providing
the FD is OK.

Any relation to Paul Menster?

Vince



On 3/23/2017 11:20 AM, [email protected] wrote:
My experience has been mainly in Ohio and Florida. Over the years, it seems the standpipe requirements have been constantly changing and confusing regarding the pressure requirements (100psi, 65 psi, etc.) and the allowance of 'Manual' standpipes. Here in Florida, the latest FBC has dropped the exception to allow manual wet standpipe in fully sprinklered buildings less than 75' in height. The current OBC also does not allow this exception. I assume this is due to the adoption of IBC. This means that almost every building that requires a standpipe, will also require a fire pump. In asking around, it seems that many people in the industry and AHJ's are either unaware of or ignore this.
My question is, what is your experience / understanding of this?
Thanks