Jerry,
I would refer the fire marshal to NFPA 13, 2016, 6.1.1.5:
6.1.1.5 Components that do not affect system performance such as
_*drain piping*_, drain valves, and signs _*shall not*_ be required
to be listed
All the emphasis is mine.
sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 03/27/2017 10:51 AM, Jerry Van Kolken wrote:
Does the drain piping have to conform to NFPA 13-6.3 after the drain
valve?
I have a system where we have connected to the drain provided by the
plumbers, but they provided ABS pipe. Now the Fire Marshal is citing
these drains as deficiencies.
Jerry Van Kolken
/_Millennium Fire Protection Corp._/
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730