Jerry,
    I would refer the fire marshal to NFPA 13, 2016, 6.1.1.5:

   6.1.1.5 Components that do not affect system performance such as
   _*drain piping*_, drain valves, and signs _*shall not*_ be required
   to be listed

    All the emphasis is mine.
sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 03/27/2017 10:51 AM, Jerry Van Kolken wrote:

Does the drain piping have to conform to NFPA 13-6.3 after the drain valve?

I have a system where we have connected to the drain provided by the plumbers, but they provided ABS pipe. Now the Fire Marshal is citing these drains as deficiencies.