More important question. Are you planning to connect to a waste line
without a receiver of some sort that provides for an approved air gap?

On Mon, Mar 27, 2017 at 11:26 AM Parsley Consulting <
[email protected]> wrote:

> Jerry,
>     I would refer the fire marshal to NFPA 13, 2016, 6.1.1.5:
>
> 6.1.1.5 Components that do not affect system performance such as *drain
> piping*, drain valves, and signs *shall not* be required to be listed
>
>     All the emphasis is mine.
> sincerely,
>
> *Ken Wagoner, SET Parsley Consulting*
>
>
>
>
> * 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone
> 760-745-6181 Visit our website <http://www.parsleyconsulting.com/> *
> On 03/27/2017 10:51 AM, Jerry Van Kolken wrote:
>
> Does the drain piping have to conform to NFPA 13-6.3 after the drain valve?
>
>
>
> I have a system where we have connected to the drain provided by the
> plumbers, but they provided ABS pipe. Now the Fire Marshal is  citing these
> drains as deficiencies.
>
>
>
> Jerry Van Kolken
>
> *Millennium Fire Protection Corp.*
>
> 2950 San Luis Rey Rd.
>
> Oceanside, CA 92058
>
> (760) 722-2722 FX 722-2730
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing 
> [email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
-- 
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to