Don't see anything in the standard or IFC that prohibits re-using demo'd pipe. Could you require that the contractor prove there is no MIC in the re-used pipe? At least that would provide a level of assurance the pipe is sound. Also, might put enough pressure on the contractor to abandon the practice or possibly even undo some of the questionable work.
Micah Davis, SET NICET #124745 Water Based Systems Layout, Level IV Dynamic Fire Designs Mail: [email protected] Mobile: 931-242-1299 www.dynamicfiredesigns.com<http://dynamicfiredesigns.com> Dynamic Fire Designs • 13063 County Line Rd., Box #87 • Spring Hill • FL • 34609 This message is confidential. It may also be privileged or otherwise protected by work product immunity or other legal rules. If you have received it by mistake, please let us know by e-mail reply and delete it from your system; you may not copy this message or disclose its contents to anyone. The integrity and security of this message cannot be guaranteed on the Internet. ________________________________ From: Sprinklerforum <[email protected]> on behalf of Reed A. Roisum, SET <[email protected]> Sent: Tuesday, April 11, 2017 12:00 PM To: [email protected] Subject: Salvaged Piping I am doing CA on a project where the contractor was allowed to “reuse” existing piping to supply new sprinklers and drops in areas of renovation. Apparently they demo’d sections of pipe and rehung to supply new sprinklers (it was obvious because the salvaged sections were painted and adjacent lengths were not:)). In my mind I shouldn’t have to do anything except say, “you can’t do that!”. However, I’ve been asked to find references in our spec and/or the codes and standards that prohibits hanging demo’d pipe. Our spec does say “Install pipes and pipe fittings in accordance with NFPA Standards.” Wondering if anyone knows of any language in NFPA 13 or elsewhere that would bolster my argument beyond saying that it is “commonly understood” or “standard practice”? My view is that we gave permission to utilize existing piping; once they removed it, the pipe became demolished piping, not existing. Unfortunately we are using the owner’s spec and not ours so there is more opportunity for shenanigans :). Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org