Love this thread- I've faced similar situations and lost every time.

In the end I agree with Steve's question of asking why we wouldn't want to
protect these areas (proactive)

Popcorn popped- carry on

 

Jeff Bridges

JBFP Inc

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Monday, April 17, 2017 7:55 AM
To: [email protected]
Subject: RE: Covered Restaurant Seating Area

 

John:

I was responding earlier from home and now, seated at my incredibly
cluttered desk, have reviewed 8.15.7 (2013 ed.).   As tactfully as I can say
this, you're reaching.  For very hard-to-grasp fruit.   I sincerely doubt
you're going to get any fire or building official to see your way to
applying an exception that describes a non-combustible envelope with wood
framing and sprinklered interstitial spaces to a vinyl or nylon canopy.  

 

In reality - and I've had to walk this line hundreds of times here in fair
weather California - the underlying reason that you're in pickle and the
owner wants to exclude sprinklers is because they don't want to deal with
the trouble and expense of designing a canopy frame that will withstand the
weight of its cover, water-filled sprinkler pipe and wind shear.  Out here,
you can add the applied horizontal force of seismic bracing as well.    In
cold weather climates, there's the challenge of having to make the system
dry, but often al fresco dining areas are built like screen rooms with hard
framing above and around, but that's a different story.    

 

Apologies for shamelessly pimping my business model, but if the architect
and owner had been indoctrinated (inoculated) regarding the need to
sprinkler such spaces early in the project (like, DESIGN PHASE), you
wouldn't inherit this interpretive challenge that puts you at risk
financially.    One of the reasons I don't miss contracting is that as a
consultant, I'm not put in the unenviable and uncomfortable position of
lobbying against sprinklers.  Why wouldn't we (proactive industry types)
want to protect areas where people are eating and drinking, and especially
where they are potentially drinking alcoholic beverages, by candlelight and
in some states still, smoking?

 

Steve L.

 

 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Monday, April 17, 2017 6:16 AM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: Covered Restaurant Seating Area

 

I suggest you run those by your local building and fire officials.

 

 

Steve

 

 

-------- Original message --------

From: John Irwin <[email protected]
<mailto:[email protected]> > 

Date: 4/17/17 6:00 AM (GMT-08:00) 

To: [email protected]
<mailto:[email protected]>  

Subject: RE: Covered Restaurant Seating Area 

 

I would disagree with this unless you can direct me to some more
information. 8.15.7.3(2) even goes on to spell out Light and Ordinary Hazard
Occupancy situations where sprinklers can be omitted.

 

John Irwin - CET

Division Manager - Fire Sprinklers

Critical System Solutions, LLC

Licence Number: FPC16-000053
Cell:     813.618.2781

Email:  [email protected]
<mailto:[email protected]> 

 



 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Monday, April 17, 2017 8:53 AM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: Covered Restaurant Seating Area

 

Overhang exceptions only apply when the area below is not used for storage
or handling of combustibles or otherwise classified as occupied by the
applicable building code or building official. As Spicey would say,
restaurant seating areas are assembly occupancy, PERIOD!

 

 

Steve

 

 

-------- Original message --------

From: John Irwin <[email protected]
<mailto:[email protected]> > 

Date: 4/17/17 5:45 AM (GMT-08:00) 

To: [email protected]
<mailto:[email protected]>  

Subject: RE: Covered Restaurant Seating Area 

 

I'm using 13 8.15.7 to argue that if the fabric covering the steel frame is
non-combustible than perhaps the sprinklers are not required.

 



 

John Irwin - CET

Division Manager - Fire Sprinklers

Critical System Solutions, LLC

Licence Number: FPC16-000053
Cell:     813.618.2781

Email:  [email protected]
<mailto:[email protected]> 

 



 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Monday, April 17, 2017 8:33 AM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: Covered Restaurant Seating Area

 

Often, we try to read the standards backwards. The way that NFPA 13 is
written, it requires sprinklers everywhere. What the client is hopeful of is
an exception but I'm pretty sure they are not going to find one for this
particular application.  If I'm taking the contrary point of view, I would
say that instead of looking for a section  that requires sprinklers here or
there,  show me where it says I don't have to put sprinklers over this
occupied area that is part of the use of the protected premises.

 

 

Steve Leyton

 

 

 

 

-------- Original message --------

From: John Irwin <[email protected]
<mailto:[email protected]> > 

Date: 4/17/17 4:11 AM (GMT-08:00) 

To: [email protected]
<mailto:[email protected]>  

Subject: Covered Restaurant Seating Area 

 

Here's the situation. Existing restaurant seating area covered by steel
frame and vinyl or nylon tarp. 100% open. Protected with sprinklers.

 

Additional covered seating area being added that will be steel frame but
insulated aluminum panel roof. 100% open.

 

Client doesn't believe sprinklers are required and wants the existing
sprinklers under the vinyl canopy removed.

 

Can someone direct me to code references?

 

 

John Irwin

Division Manager - Fire Sprinklers 

Critical System Solutions, LLC

License Number: FPC16-000053
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122

Fax:      727.209.5126

Cell:     813.618.2781

Email:  [email protected]
<mailto:[email protected]> 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to