High-rise Condo Building. Non-combustible construction.  I refer to 8.15.7.1 
which points me to 8.15.7.2. If I meet the requirements of 8.15.7.2, can I stop 
reading and omit the sprinklers on the balcony? Specifically, the penthouse 
level balconies have outdoor kitchens. It's been questioned whether or not 
these are required to be protected. I can't find anything in NFPA 101, the 
Florida Fire Prevention Code or the Florida Building Code that would be more 
restrictive than 8.15.7.2

I say the sprinkler protection is not required, outdoor kitchen or not.

Comments?