Well technically the AHJ can't require it without a city ordinance. But I'm 
directed to price to code. So if they have to be added later it would be a 
change order.



John Irwin
Division Manager - Fire Sprinklers
Critical System Solutions
[email protected]
813-618-2781


Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.

-------- Original message --------
From: Pete Schwab <[email protected]>
Date: 4/21/17 12:46 PM (GMT-05:00)
To: Charles Thurston <[email protected]>, 
[email protected]
Subject: RE: Sprinkler Protection on Balconies

John
Charles is correct for Florida as we are on NFPA 1. I believe 10.11.6.3 does 
allow the outdoor kitchen if it is permanent and in accordance with its 
listing. However, most I believe AHJ’s will require sprinkler protection.

10.11.6 Cooking Equipment.
10.11.6.1 For other than one- and two-family dwellings, no
hibachi, grill, or other similar devices used for cooking, heating, or
any other purpose shall be used or kindled on any balcony, under
any overhanging portion, or within 10 ft (3 m) of any structure.
10.11.6.2 For other than one-and two-family dwellings, no
hibachi, grill, or other similar devices used for cooking shall be
stored on a balcony.
10.11.6.3* Listed equipment permanently installed in
accordance with its listing, applicable codes, and manufacturer’s
instructions shall be permitted.
A.10.11.6.3 It is not the intent of this paragraph to allow the
permanent installation of portable equipment unless it is permitted
by its listing.


Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com<http://www.waynefire.com/>

[cid:[email protected]]

I sleep in a sprinklered home, do you?



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Charles Thurston
Sent: Friday, April 21, 2017 11:55 AM
To: [email protected]
Subject: Re: Sprinkler Protection on Balconies

Hello John,

I do belive those grills you are referring to on lower levels are not allowed. 
I know in this area they are not.

Friday, April 21, 2017, 10:56:22 AM, you wrote:

Pete, as always, your input is appreciated. One of the things I liked best 
about working for your company (way back when) was having you as a quick 
resource. Thank you for taking the time to respond.

I don’t know where to search for these Declaratory statements. I always do a 
fair amount of my own research before I send out for help.

I don’t disagree with your latter statement but question whether a grill or 
cooktop would be classified as “cooking facilities”.  For that matter, how is a 
permanent grill mounted in to a counter different from a portable grill that a 
resident on one of the lower floors might place on a balcony.

I believe my answer to the client will be that I can find no requirement to 
provide fire sprinklers on the penthouse balconies.

John Irwin - CET
Division Manager – Fire Sprinklers
Critical System Solutions, LLC
Licence Number: FPC16-000053
Cell:     813.618.2781
Email:  
[email protected]<mailto:[email protected]>

[cid:[email protected]]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Pete Schwab
Sent: Friday, April 21, 2017 10:47 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Sprinkler Protection on Balconies

John
I am going to have to start charging for my research. Here is a Declaratory 
statement for what you are asking minus the outdoor kitchens. If there is going 
to be a kitchen, I would say there will be cooking facilities and then in my 
opinion sprinklers would be required.
Pete

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com<http://www.waynefire.com/>

[cid:[email protected]]

I sleep in a sprinklered home, do you?



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Friday, April 21, 2017 9:20 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Sprinkler Protection on Balconies

High-rise Condo Building. Non-combustible construction.  I refer to 8.15.7.1 
which points me to 8.15.7.2. If I meet the requirements of 8.15.7.2, can I stop 
reading and omit the sprinklers on the balcony? Specifically, the penthouse 
level balconies have outdoor kitchens. It’s been questioned whether or not 
these are required to be protected. I can’t find anything in NFPA 101, the 
Florida Fire Prevention Code or the Florida Building Code that would be more 
restrictive than 8.15.7.2

I say the sprinkler protection is not required, outdoor kitchen or not.

Comments?

[cid:[email protected]]


John Irwin - CET
Division Manager – Fire Sprinklers
Critical System Solutions, LLC
License Number: FPC16-000053
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122
Fax:      727.209.5126
Cell:     813.618.2781
Email:  
[email protected]<mailto:[email protected]>






--
Best regards,
Charles Thurston                          [email protected]
MYRTLE BEACH FIRE SAFETY GROUP
A Division of Pye-Barker Fire Safety
1445 Cannon Road
Myrtle Beach, SC 29577
(843) 916 - 8787
(843) 839 - 3473 facsimile

[cid:[email protected]]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to