What criteria is being used to require said sprinkler. A 4 ft wide is irrelevant for a rack. What is the rack shelf area and does it comply with 16.1.6 regarding solid shelving?
Roland Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> Fire Sprinklers Saves Lives > On Apr 21, 2017, at 4:53 AM, Dewayne Martinez > <[email protected]> wrote: > > NFPA 13 (07ed) > I have an inspector that is requesting in-rack sprinklers for a single row > rack located along an outside wall because the rack shelves are wider than > 4ft (open shelve). The OHS is capable of protecting the racks W/O in-rack > sprinklers. Is there something in NFPA to address this either way? > Thanks, > Dewayne > _______________________________________________ > Sprinklerforum mailing list > [email protected] > <mailto:[email protected]> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>