Are you using an alarm valve or a water flow switch?  Are you connected to an 
alarm monitoring system or is it only local alarm bells that you are trying to 
ring?



Cliff



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Cesar Lira
Sent: Monday, April 24, 2017 6:13 PM
To: [email protected]
Subject: RE: TIME OF INITIATE AN ALARM



Wet.



De: Sprinklerforum [mailto:[email protected]] En 
nombre de Matt Grise
Enviado el: lunes, 24 de abril de 2017 03:27 p. m.
Para: [email protected] 
<mailto:[email protected]>
Asunto: RE: TIME OF INITIATE AN ALARM



Wet system or dry?



Matt





From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Cesar Lira
Sent: Monday, April 24, 2017 4:38 PM
To: [email protected] 
<mailto:[email protected]>
Subject: TIME OF INITIATE AN ALARM



FM say, that any fire alarm shall initiate within 60 seconds.

How can I get in calculations the time of the alar respond? My system is too 
large and the insurance company is question to me about if I’m sure that alarm 
shall sound in this time.



Thks. Everybody.