Cesar, first I don't know the exact wording of the requirement you cited. 

 

The size of the system does not in itself affect the time from the start of 
water flowing until the alarm is initiated. Air in the system, however, 
definitely can affect delay time. This is because no water flows past the alarm 
valve or waterflow detector, until system pressure is reduced as air forces 
water out of the system.More air in the system causes longer delay time. Once 
supply and system water pressures equalize, the retarding mechanism of a 
waterflow detector or the delay due to the filling of a retard chamber adds 
more time to the delay.

 

You can have an inspectors test valve opened, and count the time it takes to 
open the alarm valve.  If you are using a waterflow indicator you can remove 
its cover and watch the extension arm. This time is the part of the delay 
caused by air in the system. There will be no alarm until the retard time of 
the waterflow indicator or the retard chamber has had its effect.

 

The retard time of the retard chamber is usually fixed.  For an electric alarm, 
a switch is often mounted on top of the retard chamber.  Some switches have an 
additional time delay capability.  If so, this time must be added to the 
others. If your system does not meet the required time limit, delay time of the 
riser delay functions must get first attention. If these functions are causing 
too much delay, corrections must be made. Nothing you could to about the amount 
of air in the system would get you to an acceptable level.  If the alarm device 
delays are within the time limits, but overall time is too long, the air effect 
must be attended to.  If a system is emptied, and water returned without there 
being any water flowing out of the system, all the air in the system is 
compressed.This can result in long delay times. If water is being discharged 
(as through a remote inspectors valve) some air can be discharged, prior to 
water coming out the outlet.  It is best, then, to keep a remote ITV open when 
filling the system.This does hot help, though, if the ITV is at the riser. One 
or more air release valves can be used to automatically remove unwanted air. 
Google sprinkler air release valve to learn more about them.

 

On Mon, Apr 24, 2017 at 5:13 PM, Cesar Lira <[email protected] 
<mailto:[email protected]> > wrote:

We are considering both, alarm valve and water flow switch connect to an alarm 
monitoring system.

 

De: Sprinklerforum [mailto:[email protected] 
<mailto:[email protected]> ] En nombre de Cliff 
Whitfield
Enviado el: lunes, 24 de abril de 2017 05:48 p. m.
Para: [email protected] 
<mailto:[email protected]> 
Asunto: RE: TIME OF INITIATE AN ALARM

 

Are you using an alarm valve or a water flow switch?  Are you connected to an 
alarm monitoring system or is it only local alarm bells that you are trying to 
ring?

 

Cliff

 

From: Sprinklerforum [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of Cesar 
Lira
Sent: Monday, April 24, 2017 6:13 PM
To: [email protected] 
<mailto:[email protected]> 
Subject: RE: TIME OF INITIATE AN ALARM

 

Wet.

 

De: Sprinklerforum [mailto:[email protected]] En 
nombre de Matt Grise
Enviado el: lunes, 24 de abril de 2017 03:27 p. m.
Para: [email protected] 
<mailto:[email protected]> 
Asunto: RE: TIME OF INITIATE AN ALARM

 

Wet system or dry?

 

Matt 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Cesar Lira
Sent: Monday, April 24, 2017 4:38 PM
To: [email protected] 
<mailto:[email protected]> 
Subject: TIME OF INITIATE AN ALARM

 

FM say, that any fire alarm shall initiate within 60 seconds.

How can I get in calculations the time of the alar respond? My system is too 
large and the insurance company is question to me about if I’m sure that alarm 
shall sound in this time.

 

Thks. Everybody.

CLR

 

 

 


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
 

Virus-free.  
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>
 www.avast.com 

 


_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





 

-- 

Ed Vining

4819 John Muir Rd

Martinez CA 94553

925-228-8792 <tel:(925)%20228-8792> 

Cell 925-787-0465 <tel:(925)%20787-0465> 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to