3.3.1 (13 edition of 13R) States, lavatory or water closet.

Lavatory  = sink
Water Closet = toilet.

So yes, bathroom.

R/
Matt



Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:[email protected]]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bob
Sent: Friday, April 28, 2017 11:40 AM
To: [email protected]
Subject: 13R SINK ROOM

NFPA 13R states (2013), "A.6.6.2   A room is still considered a bathroom if it 
contains just a toilet. Additionally, two bathrooms can be adjacent to
each other and are considered separate rooms, provided they are enclosed with 
the required level of construction."

Would the room adjacent to the Bath Room that is 22 sf and only contains a sink 
still be considered a Bath Room, or does it require a sprinkler?

Thank you,

Bob Knight, CET III
208-318-3057
[FBK-LOGO-SMALL]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to