>From past experience the annex carries no weight when it comes to standards, 
>that's all I'm saying. You could turn your question around and say "please 
>provide a reference in the standard that allows pipe to be supported from 
>pipe."

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ryan Labrie
Sent: Monday, May 01, 2017 9:36 AM
To: [email protected]
Subject: RE: Hanging Pipe off system Piping

Please provide the reference that states sprinkler components cannot be 
supported by sprinkler components. Only interpretations of various sections 
have been provided so far.

Ryan Labrie
Fire Protection Designer

Critical System Solutions, LLC
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122
Fax:      727.209.5126
Cell:     813.394.3978
Email:  
[email protected]<mailto:[email protected]>

[CSS Logo]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Monday, May 1, 2017 8:31 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Hanging Pipe off system Piping

Just thinking out loud but with that "allowance" being made in the Annex and 
not in the Standard itself is it really enforceable?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Denhardt
Sent: Monday, May 01, 2017 7:14 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Hanging Pipe off system Piping

I also agree.  When I read Ken's comments on Friday, I thought I must have been 
wrong in the past because I know I have done/allowed it.  I wanted to check 
this morning and as Ryan stated if 9.1.1.2 is satisfied, it is allowed.

John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
4011 Penn Belt Place
Forestville, Maryland 20747-4737
301.474.1136 - Office
301.343.1457 - Mobile



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ryan Labrie
Sent: Monday, May 01, 2017 6:55 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Hanging Pipe off system Piping

Ken,

I would have to disagree with your interpretation. I believe it is actually 
specifically allowed if the requirements of 9.1.1.2 are met.

NFPA 13-2016/2013 A.9.1.1.8.1 2010 A9.1.1.7
The rules covering the hanging of sprinkler piping take into consideration the 
weight of water-filled pipe plus a safety factor. No allowance has been made of 
the hanging of non-system components from sprinkler piping. NFPA 13 provides 
the option  to support sprinkler piping from other sprinkler piping where the 
requirement of 9.1.1.2 are met.

Ryan Labrie
Fire Protection Designer

Critical System Solutions, LLC
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122
Fax:      727.209.5126
Cell:     813.394.3978
Email:  
[email protected]<mailto:[email protected]>

[CSS Logo]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Parsley Consulting
Sent: Friday, April 28, 2017 3:56 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Hanging Pipe off system Piping

Jerry,

    If I understand you correctly, in that a hanger assembly on an armover is 
attached only to other sprinkler piping, it is indeed contrary to the 
requirements of NFPA 13, 9.2.1.3, which notes:
9.2.1.3.1 Sprinkler piping shall be substantially supported from the building 
structure, which must support the added
load of the water-filled pipe plus a minimum of 250 lb (115 kg) applied at the 
point of hanging, except where permitted by 9.2.1.1.2, 9.2.1.3.3, and 9.2.1.4.1.
    It would take a significant separation from structural engineering 
principals to regard other sprinkler piping as being an equivalent to the 
building structure.

    Indeed, the very next section, 9.2.1.3.2, states:
9.2.1.3.2 Trapeze hangers shall be used where necessary to transfer loads to 
appropriate structural members.
    Simply put, sprinkler piping has to be supported by the building structure.

    As I'm a member of the hanging and bracing committee please see the 
disclaimer below.
sincerely,
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit our website<http://www.parsleyconsulting.com/>

IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued 
pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of 
the author and does not necessarily represent the official position of the NFPA 
or its Technical Committees. In addition, this correspondence is neither 
intended, nor should it be relied upon, to provide professional consultation or 
services

It should be noted that the above is my opinion as a member of the NFPA 
Automatic Sprinkler System Hanging and Bracing Committee in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the NFPA or its 
Committees



On 04/28/2017 11:53 AM, Jerry Van Kolken wrote:
We recently did a survey, and a question of legitimacy in the current 
installation of some piping supports came up. This system had a branchline with 
a drop to an arm-over that ran directly under the branchine. The arm-over is 
being supported by the branchline.

Is this allowed?

I personally think this is a bad installation but I skimmed the code and 
couldn't find the answer one way or other.

Jerry Van Kolken
Millennium Fire Protection Corp.
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730



_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to