I’ve stayed out of this one because folks way smarter than me are already 
engaged.

Seems to me that if you can satisfy the metrics Roland alludes to in his 
preceding post, and get the design signed off by a structural engineer, there’s 
no reason it won’t work … at least in theory.  But my experience (as a resident 
of a seismically hyperactive city and state) is that many structural engineers 
get a little janky when you tell them they have to evaluate the structure and 
two different hanger assemblies for all of that cumulative “adequacy”.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Monday, May 01, 2017 11:14 AM
To: [email protected]
Subject: Re: Hanging Pipe off system Piping

13 ALLOWS it in 9.1.1.8.1 (in the body) by saying shall not support NON-SYSTEM 
components.  That means other system components can be supported.  Then the 
annex further clarifies that yes indeed this includes system piping.  I think 
this mainly started with hanging activation components for water spray systems.

The main caveat is that the upper hanger must be sized to include the weight of 
the lower pipe (which naturally is 5 times the actual weight).  I would argue 
that the 250 is only added once since you should not have two guys hanging in 
the same space (containing both pieces of pipe) at the same time.

Just my opinion and not to be considered a formal interpretation of the NFPA or 
any of its technical committees.


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.
Dallas, TX
http://www.firesprinkler.org<http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives



On Apr 28, 2017, at 11:53 AM, Jerry Van Kolken 
<[email protected]<mailto:[email protected]>> wrote:

We recently did a survey, and a question of legitimacy in the current 
installation of some piping supports came up. This system had a branchline with 
a drop to an arm-over that ran directly under the branchine. The arm-over is 
being supported by the branchline.

Is this allowed?

I personally think this is a bad installation but I skimmed the code and 
couldn’t find the answer one way or other.

Jerry Van Kolken
Millennium Fire Protection Corp.
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to