Can you use the remote area reduction utilizing quick response heads and
the other criteria mentioned in 11.2.3.2.3.1.  This is in the 2010 edition
I dont have the 13 edition in front of me right now.

On Wed, May 3, 2017 at 3:54 PM, Micah Davis, SET <
[email protected]> wrote:

> I have a mixed use Retail/Residential building protected per NFPA 13. I am
> calcing the retail area at 0.20 gpm. The space is not large enough to get
> the full 1500 sq ft so I have a few heads in the adjacent corridor in the
> calcs to make up the difference. Normally, I calc the OH heads at 0.20
> gpm/sq ft and the LH heads at 0.10 gpm/sq ft. However, the engineer has
> asked me to calc the LH heads at the 0.20 gpm rate since the wall
> separating the two areas is not a rated wall. The problem I have with this
> is that the LH heads are spaced for LH occupancy so they will become the
> most demanding sprinklers (14 ft x 12 ft spacing = 168 sq ft x 0.20 gpm =
> 33.6 gpm as opposed to the OH heads at 125 sq ft x 0.20 gpm = 25 fpm). This
> doesn't seem right, but I cannot find a foothold in the standard to begin
> the "discussion". 2013 edition is the adopted standard and it reads "Each
> sprinkler in the design area and the remainder of the hydraulically
> designed system shall discharge at a flow rate at least equal to the
> stipulated minimum water application rate (density) multiplied by the area
> of sprinkler operation (23.4.4.6.1)" This seems to support his request. Any
> help out there?
>
>
> Thank you,
> Micah Davis
> www.dynamicfiredesigns.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>


-- 
Shawn Foor, SET

*FOOR DESIGN, LLC*
*6227 S. 87TH E. AVE*
*TULSA, OK 74133*
*P:918-237-1400*
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to