Roland

I think that is what I was looking for.  If I am reading this correctly, the 
wall separating the two spaces qualifies even though it is not rated.  The only 
requirement is that it prevents the heat from fusing the heads, not that it is 
capable of preventing the fire from spreading to the other side of the 
partition as a rated wall would.  Thank you!


Micah Davis

www.dynamicfiredesigns.com



________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Roland Huggins <[email protected]>
Sent: Wednesday, May 3, 2017 4:01 PM
To: [email protected]
Subject: Re: Remote Area w/ OH & LH sprinklers

Look at A.11.1.2 for having different densities within one remote area.  Don’t 
forget the 15 ft overlap (or wall) required between different hazard 
classifications (the body portion of 11.1.2)

Roland



Roland Huggins, PE - Senior VP Engineering

American Fire Sprinkler Assn.

Dallas, TX

http://www.firesprinkler.org<http://www.firesprinkler.org/>

[https://www.firesprinkler.org/wp-content/themes/onlywebsites/images/01.jpg]<http://www.firesprinkler.org/>

American Fire Sprinkler Association (Information & 
Resources)<http://www.firesprinkler.org/>
www.firesprinkler.org
Representing fire sprinkler industry offering expert technical support, 
education and training, yearly convention and exhibit for fire sprinkler 
contractors



Fire Sprinklers Saves Lives




On May 3, 2017, at 1:54 PM, Micah Davis, SET 
<[email protected]<mailto:[email protected]>> 
wrote:

I have a mixed use Retail/Residential building protected per NFPA 13. I am 
calcing the retail area at 0.20 gpm. The space is not large enough to get the 
full 1500 sq ft so I have a few heads in the adjacent corridor in the calcs to 
make up the difference. Normally, I calc the OH heads at 0.20 gpm/sq ft and the 
LH heads at 0.10 gpm/sq ft. However, the engineer has asked me to calc the LH 
heads at the 0.20 gpm rate since the wall separating the two areas is not a 
rated wall. The problem I have with this is that the LH heads are spaced for LH 
occupancy so they will become the most demanding sprinklers (14 ft x 12 ft 
spacing = 168 sq ft x 0.20 gpm = 33.6 gpm as opposed to the OH heads at 125 sq 
ft x 0.20 gpm = 25 fpm). This doesn't seem right, but I cannot find a foothold 
in the standard to begin the "discussion". 2013 edition is the adopted standard 
and it reads "Each sprinkler in the design area and the remainder of the 
hydraulically designed system shall discharge at a flow rate at least equal to 
the stipulated minimum water application rate (density) multiplied by the area 
of sprinkler operation (23.4.4.6.1)" This seems to support his request. Any 
help out there?

Thank you,
Micah Davis
www.dynamicfiredesigns.com<http://www.dynamicfiredesigns.com/>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to