Roland I think that is what I was looking for. If I am reading this correctly, the wall separating the two spaces qualifies even though it is not rated. The only requirement is that it prevents the heat from fusing the heads, not that it is capable of preventing the fire from spreading to the other side of the partition as a rated wall would. Thank you!
Micah Davis www.dynamicfiredesigns.com ________________________________ From: Sprinklerforum <[email protected]> on behalf of Roland Huggins <[email protected]> Sent: Wednesday, May 3, 2017 4:01 PM To: [email protected] Subject: Re: Remote Area w/ OH & LH sprinklers Look at A.11.1.2 for having different densities within one remote area. Don’t forget the 15 ft overlap (or wall) required between different hazard classifications (the body portion of 11.1.2) Roland Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firesprinkler.org<http://www.firesprinkler.org/> [https://www.firesprinkler.org/wp-content/themes/onlywebsites/images/01.jpg]<http://www.firesprinkler.org/> American Fire Sprinkler Association (Information & Resources)<http://www.firesprinkler.org/> www.firesprinkler.org Representing fire sprinkler industry offering expert technical support, education and training, yearly convention and exhibit for fire sprinkler contractors Fire Sprinklers Saves Lives On May 3, 2017, at 1:54 PM, Micah Davis, SET <[email protected]<mailto:[email protected]>> wrote: I have a mixed use Retail/Residential building protected per NFPA 13. I am calcing the retail area at 0.20 gpm. The space is not large enough to get the full 1500 sq ft so I have a few heads in the adjacent corridor in the calcs to make up the difference. Normally, I calc the OH heads at 0.20 gpm/sq ft and the LH heads at 0.10 gpm/sq ft. However, the engineer has asked me to calc the LH heads at the 0.20 gpm rate since the wall separating the two areas is not a rated wall. The problem I have with this is that the LH heads are spaced for LH occupancy so they will become the most demanding sprinklers (14 ft x 12 ft spacing = 168 sq ft x 0.20 gpm = 33.6 gpm as opposed to the OH heads at 125 sq ft x 0.20 gpm = 25 fpm). This doesn't seem right, but I cannot find a foothold in the standard to begin the "discussion". 2013 edition is the adopted standard and it reads "Each sprinkler in the design area and the remainder of the hydraulically designed system shall discharge at a flow rate at least equal to the stipulated minimum water application rate (density) multiplied by the area of sprinkler operation (23.4.4.6.1)" This seems to support his request. Any help out there? Thank you, Micah Davis www.dynamicfiredesigns.com<http://www.dynamicfiredesigns.com/> _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org