Confirmed - light hazard.

John August Denhardt, P.E.
Strickland Fire Protection

On May 10, 2017, at 7:13 AM, Richard Carr 
<[email protected]<mailto:[email protected]>> wrote:

Yes, unused attic is light hazard but you are limited on head spacing.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
[email protected]<mailto:[email protected]>
904-781-8227

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Stossel
Sent: Wednesday, May 10, 2017 7:11 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Sloped Roof in ESFR system

I am currently working on an old wood building that my client wants to use for 
rack storage.  The building has a sloped roof that exceeds the allowable pitch 
so they will be installing a dropped ceiling to create the flat surface.  The 
area above the ceiling will now be a combustible concealed space that needs 
protection.  Nothing will be stored above the ceiling, would the area above the 
ceiling be considered light hazard?  From everything that I can find, I believe 
it would be, but I would appreciate the forums input.

Thanks,

Mike Stossel SET
<image001.png>
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
[email protected]<mailto:[email protected]>

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to