Confirmed - light hazard. John August Denhardt, P.E. Strickland Fire Protection
On May 10, 2017, at 7:13 AM, Richard Carr <[email protected]<mailto:[email protected]>> wrote: Yes, unused attic is light hazard but you are limited on head spacing. Richard Carr, SET Branch Manager Cox Fire Protection, Inc 6555 Grace Lane. Jacksonville, Fl. 32205 [email protected]<mailto:[email protected]> 904-781-8227 From: Sprinklerforum [mailto:[email protected]] On Behalf Of Mike Stossel Sent: Wednesday, May 10, 2017 7:11 AM To: [email protected]<mailto:[email protected]> Subject: Sloped Roof in ESFR system I am currently working on an old wood building that my client wants to use for rack storage. The building has a sloped roof that exceeds the allowable pitch so they will be installing a dropped ceiling to create the flat surface. The area above the ceiling will now be a combustible concealed space that needs protection. Nothing will be stored above the ceiling, would the area above the ceiling be considered light hazard? From everything that I can find, I believe it would be, but I would appreciate the forums input. Thanks, Mike Stossel SET <image001.png> 36 Barren Road East Stroudsburg, PA 18302 Office: 973-670-2627 [email protected]<mailto:[email protected]> _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org