As mentioned the cost savings from deviations from the datasheet criteria is 
often offset by an increase in the insurance premiums (so there is little 
incentive to allow a deviation after the price has been agreed 😊). 

 

I have not had much success with getting deviations to the non-flat obstruction 
criteria. I suppose it’s better they were spending the money on sprinklers than 
additional insurance premiums but it can be a shock to the system when working 
with clients from previous projects from before this criteria came in. (further 
complicated by the “Grouped Obstruction” criteria) Maybe different in different 
areas and depending on who the FM rep is. My experience with FM has primarily 
been in the EU. Would be interested to hear if other have had much luck in this 
regards.

 

Damien Shannon. 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike B Morey
Sent: 01 June 2017 08:48
To: [email protected]
Subject: RE: Review Comments

 

100% agree, my last stop our only client was a major FM insured site, it took a 
lot of prodding but they started pushing back more and more as FMs requirements 
became more and more onerous to their pocketbook.  The real tipping point was 
the 4'-0" on center heads under non-flat obstructions over 4'.  I did find the 
requirement mentioned in FM datasheet 2-0 Revised in 2014 under 2.5.2.1 (we 
should always remember to cite "chapter and verse" as my last boss would say, I 
had to look it up).  Interestingly in my 6 years at said FM client, this NEVER 
came up even once.  Underwriters are underwriters, their enforcement power is 
limited to increasing policy costs, or revoking policies for non-compliance.  
Owners need to be reminded/taught this and given their options form the 
contractor cost wise so they can see what if any cost impact the insurance 
requirement not being satisfied will create.



  _____  


Mike Morey 
CFPS 3229 • NICET S.E.T. 123677 
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company 
7614 Opportunity Drive • Fort Wayne, IN • 46825 
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected] <mailto:[email protected]> 







From:        "Prahl, Craig/GVL" <[email protected] 
<mailto:[email protected]> > 
To:        "[email protected] 
<mailto:[email protected]> " 
<[email protected] 
<mailto:[email protected]> > 
Date:        06/01/2017 10:26 AM 
Subject:        RE: Review Comments 
Sent by:        "Sprinklerforum" 
<[email protected] 
<mailto:[email protected]> > 

  _____  




FM adherence is not a requirement unless you’re directed by the OWNER to adhere 
to FM recommendations.  Just because FM publishes a Data Sheet doesn’t mean 
every portion will necessarily be followed.   

  

The specifications should explicitly state what is to be followed and to what 
degree as this should have been agreed upon by the owner and their FM rep. and 
then communicated to the EOR and included in the engineering documents prior to 
bids. 

  

Some owners will accept all insurer recommendations, others push back and take 
some and disregard other recommendations made by their insurer.  But that’s 
between the owner and insurer, not the contractor at the end of the line.   

  

Any EOR worth his fee should be asking the owner at the beginning of the 
project who their insurer is and what unique requirements are expected for the 
project.  It’s irritating to get drawings that state something like “Follow FM 
Global guidelines”.  Follow what to what end?   

  

FM’s recommendations are based on solid testing and verification of data but 
some of the recommendations do have an upcharge attached to them.  The engineer 
assigned to producing the fire protection package should be competent enough to 
understand the ramifications of insurer requirements/recommendations and 
incorporate those into the design package.  Don’t make the contractor do your 
work or have to guess.   

  

This is an issue that gets overlooked a lot by engineers and not just FP 
engineers. All engineers on projects should understand how to work with the 
owner’s insurer since FM for example has data sheets on numerous other building 
systems other than just fire protection. 

  


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540 

Fax - 864.920.7129 

CH2MHILL Extension  77540
[email protected]

  

From: Sprinklerforum [ <mailto:[email protected]> 
mailto:[email protected]] On Behalf Of Brian Harris
Sent: Thursday, June 01, 2017 10:00 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: RE: Review Comments [EXTERNAL] 

  

Luckily not an FM project. 

  

Brian Harris, CET 

BVS Systems Inc. 

 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__bvssystemsinc.com_&d=DwMGaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=yzyaR_wTcUN47wSsKMhyb_ze3PfLngCfDQqVpXLZLEU&s=D4m7VjWT3C_aoQIhjuC17qwalKt1pnJenZ9wKzkN6QQ&e=>
 bvssytemsinc.com 

  

From: Sprinklerforum [ <mailto:[email protected]> 
mailto:[email protected]] On Behalf Of Travis Mack
Sent: Thursday, June 01, 2017 9:59 AM
To:  <mailto:[email protected]> 
[email protected]
Subject: Re: Review Comments 

  

Yes. That comes straight from FM. If you have an FM job, you will be held to 
that requirement. 

Travis Mack, SET 

MFP Design, LLC 

"Follow" us on Facebook:  
<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.facebook.com_pages_MFP-2DDesign-2DLLC_92218417692&d=DwMGaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=yzyaR_wTcUN47wSsKMhyb_ze3PfLngCfDQqVpXLZLEU&s=n12MxBOn5aHmBrDb7VgHKk5KKRJnmeIJCzWDpuww1IE&e=>
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692 

Send large files to MFP Design via: 

 
<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign&d=DwMGaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=yzyaR_wTcUN47wSsKMhyb_ze3PfLngCfDQqVpXLZLEU&s=oVeid6XRQ4FRl-TLkeiuNkTFqTY6tC8kLrsgiBvf7UA&e=>
 https://www.hightail.com/u/MFPDesign 

  

Sent from my iPhone 


On Jun 1, 2017, at 6:31 AM, Damien Shannon < <mailto:[email protected]> 
[email protected]> wrote: 
That is a requirement in FM Datasheet 2-0. Is it an FM project? Was it 
specified in project specs? Can you use seamless pipe to bypass the issue? 

  

Damien Shannon. 

  

From: Sprinklerforum [ <mailto:[email protected]> 
mailto:[email protected]] On Behalf Of Brian Harris
Sent: 01 June 2017 06:59
To:  <mailto:[email protected]> 
[email protected]
Subject: Review Comments 

  

Just got back some review comments for a project we’re doing and one in 
particular stuck out; 

“Orient longitudinal pipe weld seam toward building roof; at least 45 degrees 
in relationship to the floor (for reference, the weld line points to the floor 
at 0 degrees) to mitigate pipe weld seam corrosion.” 

  

Could you imagine the headache that would cause at the fab shop? 

  

Brian Harris, CET 

BVS Systems Inc. 

Design Manager 

 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__bvssystemsinc.com_&d=DwMGaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=yzyaR_wTcUN47wSsKMhyb_ze3PfLngCfDQqVpXLZLEU&s=D4m7VjWT3C_aoQIhjuC17qwalKt1pnJenZ9wKzkN6QQ&e=>
 bvssystemsinc.com 

Phone: 704.896.9989 

Fax: 704.896.1935 

  
_______________________________________________
Sprinklerforum mailing list
 <mailto:[email protected]> 
[email protected]
 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMGaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=yzyaR_wTcUN47wSsKMhyb_ze3PfLngCfDQqVpXLZLEU&s=gcC7YInrqa8KtrGsHOm6RMAyxl8Ai7D3ntB2Qttaa5k&e=>
 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=yzyaR_wTcUN47wSsKMhyb_ze3PfLngCfDQqVpXLZLEU&s=gcC7YInrqa8KtrGsHOm6RMAyxl8Ai7D3ntB2Qttaa5k&e=>
 
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=yzyaR_wTcUN47wSsKMhyb_ze3PfLngCfDQqVpXLZLEU&s=gcC7YInrqa8KtrGsHOm6RMAyxl8Ai7D3ntB2Qttaa5k&e=
 

This message is for the named person's use only. It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission. If you receive this message in error, 
please immediately delete it and all copies of it from your system, destroy any 
hard copies of it and notify the sender. You must not, directly or indirectly, 
use, disclose, distribute, print, or copy any part of this message if you are 
not the intended recipient.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to