NFPA 13 section 11.2.3.2.2.2 states that QR sprinklers shall not be permitted 
for use in extra hazard occupancies.

Section 12.6.6 states that the use of QR sprinklers shall be permitted when 
listed for such use.

So, if I have a storage occupancy where the appropriate design criteria table 
directs me to use an Extra Hazard design curve, can I use QR sprinklers 
(assuming they are listed for storage use)?

I believe the answer would be “yes”, but looking for some feedback.

Thanks.

-Kyle M
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to