The CRR (corrosion resistance ratio) is solely based on wall thickness:

CRR = (X / Y)^3

Where:
X is the thickness of the pipe in question at the first exposed thread OR 
THINNEST WALL SECTION FOR UNTHREADED PIPE.

And

Y is the thickness of schedule 40 pipe under the first exposed thread.

So if you are roll-grooving the pipe, schedule 10 or even schedule 7 can have a 
CRR of 1 or greater. You aren’t trying to thread 10” pipe, are you?

CRR is simply a mathematical formula that has absolutely nothing to do with the 
chemical makeup of the pipe. While galvanizing or MIC-coating might help the 
pipe resist corrosion, it does not affect the CRR.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Carr
Sent: Friday, August 11, 2017 6:22 AM
To: [email protected]
Subject: RE: [EXTERNAL] RE: 10" pipe with 1.0 CRR

I thought that as a manufacturing standard all steel pipe regardless of 
schedule had to have a CRR of 1 or greater.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
[email protected]<mailto:[email protected]>
904-781-8227

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark.Phelps
Sent: Friday, August 11, 2017 9:00 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: [EXTERNAL] RE: 10" pipe with 1.0 CRR

Isn't the CRR based on the actual remaining wall thickness at the root of the 
first exposed thread outside of a fitting? So if you're not threading it, it 
should theoretically have a CRR greater than 1.0. Also, I believe the term 
Standard wall pipe in 10" diameter refers to schedule 30.

Mark at Aero
602 820-7894

Sent from my iPad

On Aug 11, 2017, at 5:49 AM, Mike Stossel 
<[email protected]<mailto:[email protected]>> wrote:
It has always been my understanding that the corrosion resistance ratio 
benchmark of (1) is based on threaded schedule 40 steel, so I believe any other 
pipe type would have a better or worse ratio, but not the same.

Mike Stossel SET
<image002.png>
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Friday, August 11, 2017 8:39 AM
To: 
[email protected]<mailto:[email protected]>
Cc: [email protected]<mailto:[email protected]>
Subject: 10" pipe with 1.0 CRR

Anyone know of 10in non-sch40 pipe that has a CRR of 1?  Have a project where 
the EOR is insisting on this.  They also have a 100lb maximum point load per 
hanger…..but that is a conversation for another day!
Thanks,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

<image004.jpg>


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to