I received more information…

Existing dry system above a stairwell.  They are adding a gyp ceiling 6 or 8’ 
below wood joist structure creating a combustible concealed space.  I can’t 
find anything that says that they have to provide access to those 
sprinklers…probably only 4-6 heads.

I guess another option would be to add gyp to the bottom of the joists and fill 
above with insulation.

Thanks for the input.


Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Tuesday, August 15, 2017 11:53 AM
To: [email protected]
Subject: RE: Sprinkler Accessibility

I would say “no”. I have installed many combustible concealed space heads that 
are hard to reach.

Matt


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Reed A. Roisum, SET
Sent: Tuesday, August 15, 2017 11:48 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Sprinkler Accessibility

Do all sprinklers have to be accessible?  If so, does anyone have reference?

Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to