Guess I was meaning accessible in the NFPA defined way, “Spaces or concealed 
areas of construction that can be entered via openable panels, doors hatches, 
or other readily movable elements (e.g., ceiling tiles).”

I’d have to argue the “everything is doable” notion also ☺.


Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Tuesday, August 15, 2017 4:27 PM
To: [email protected]
Subject: Re: Sprinkler Accessibility

Everything is ultimately accessible just like everything is doable. The 
question is how much do you want to spend (or have to spend).

On Tue, Aug 15, 2017 at 10:50 AM Matthew J Willis 
<[email protected]<mailto:[email protected]>> wrote:
I see your catch 44,

However, they are subject to the Maintenance aspect of 25.

Just a little D.A…

R/
Matt


Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:[email protected]]



From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Scott Futrell
Sent: Tuesday, August 15, 2017 11:23 AM

To: 
[email protected]<mailto:[email protected]>
Subject: RE: Sprinkler Accessibility

Another question. Because they aren’t visible, they aren’t subject to an NFPA 
25 inspection, so does it really matter?

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Tuesday, August 15, 2017 12:09 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Sprinkler Accessibility

Another question, if it is a concealed space, how do you know they are there 
and what age? Head box is one way, but very unpredictable..

R/
Matt



Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:[email protected]]



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Tuesday, August 15, 2017 11:06 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Sprinkler Accessibility

A good point. I guess that would be a pretty costly inspection?

Matt


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Scott Futrell
Sent: Tuesday, August 15, 2017 12:01 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Sprinkler Accessibility

Agreed, Matt, but how do you perform the required twenty year testing of QR 
sprinklers in a combustible concealed space? Just a question for debate…

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Tuesday, August 15, 2017 11:53 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Sprinkler Accessibility

I would say “no”. I have installed many combustible concealed space heads that 
are hard to reach.

Matt


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Reed A. Roisum, SET
Sent: Tuesday, August 15, 2017 11:48 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Sprinkler Accessibility

Do all sprinklers have to be accessible?  If so, does anyone have reference?

Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
Sent from Gmail Mobile

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to