Correct. That seems to be a fallacy that people locked on to long ago and never 
let go of. NFPA 13D is for one and two family dwellings. For a single family 
home it is not required. If you are doing a duplex (a two family dwelling) then 
you add the demand. 



Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Aug 17, 2017, at 8:53 PM, Owen Evans <[email protected]> wrote:
> 
> I have always added 5 gpm domestic flow at the riser when calculating a 13D 
> system for a SFR.  Last night I was having a hard time falling asleep so I 
> thought I would break out the 2016 edition of 13D and start reading, surely I 
> would fall asleep quickly. I got to 6.5 Common Supply Pipes, 6.5.2 which 
> states; In common water supply connections servicing more that one dwelling 
> unit, 5 gpm shall be added to the sprinkler system demand to determine the 
> size of common piping and the size of the total water supply 
> requirements...yada, yada, yada.
> 
> So reading 6.5.2 I interpret that if it is a SFR (one unit) I am not required 
> to add 5 gpm domestic into the calculations, correct?
> 
> Owen Evans
> 
> 