Hi
 
we flow switch and relay to isolate the sprinkler if there is a demand
 
 
-----Original Message-----
From: Travis Mack <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Fri, Aug 18, 2017 11:16 am
Subject: Re: NFPA 13D - Adding 5 gpm Domestic Flow in Calculations



Yes. We do have some authorities that mandate it. But it is still above the 
minimum requirements of 13D. 


I always thought it was odd. But there are many things some authorities require 
that I feel are odd. Ha ha. 


Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign


Sent from my iPhone

On Aug 18, 2017, at 7:39 AM, Parsley Consulting <[email protected]> 
wrote:



              I believe the mandate        for a 5 gpm addition for domestic 
demand was added for single        family homes by some jurisdictions as a rule 
of thumb quite some        time back.  And, to put a fine point on it, Owen, 
it's state law        in California, so yes you certainly are required        
to add 5 gpm flow for domestic if the building is a single        family home.  
        
        From the 2016 edition of the California Residential          Code 
[emphasis mine]:
          
R313.3.5          Water supply. The water supply shall provide not less than 
the          required design flow rate for sprinklers in accordance with        
  Section R313.3.4.2 at a pressure not less than that used to          comply 
with Section R313.3.6. Where a water supply              serves both domestic 
and fire sprinkler systems, 5 gpm (19              L/min) shall be added to the 
sprinkler system demand          at the point where the systems are connected, 
to determine the          size of common piping and the size of the total water 
supply          requirements where no provision is made to prevent flow into    
      the domestic water system upon operation of a sprinkler.
    
    Now this isn't to        suggest that some AHJ's won't apply this in a 
different manner.         From a recent plan review rejection notice in 
California:
          
Revise the hydraulic calculations for        the companion unit to account for 
the hose demand for the 2        story dwelling unit and the companion unit, 5 
+ 5 = 10 gpm. w/        sprinklers it should be 44.4 gpm. There is only one 
underground        lateral serving both dwellings. 
      
    What this goes to show,        I suppose, is that it depends on where the 
property is located        as to whether or not that 5 gpm domestic allowance 
is required.         Before I submitted a hydraulic calculation omitting that 
value        I'd make absolutely certain that it were not required by state     
   or local ordinance.
        
        sincerely,
          
Ken Wagoner,          SET
          Parsley Consulting
          350 West 9th Avenue, Suite 206
            Escondido, California 92025
             Phone                760-745-6181
             Visit              the website
              
             
    
On 08/17/2017 9:01 PM, Travis Mack      wrote:
    
    
            
Correct. That seems to be a fallacy that people locked on to        long ago 
and never let go of. NFPA 13D is for one and two family        dwellings. For a 
single family home it is not required. If you        are doing a duplex (a two 
family dwelling) then you add the        demand. 
      

      
      

        
        
Travis Mack, SET
        
MFP Design, LLC
        
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
        
Send large files to MFP Design via:
        
https://www.hightail.com/u/MFPDesign
        

        
        Sent from my iPhone
      

        On Aug 17, 2017, at 8:53 PM, Owen Evans <[email protected]>        wrote:
        
      
      
        
I have always            added 5 gpm domestic flow at the riser when 
calculating a            13D system for a SFR.  Last night I was having a hard 
time            falling asleep so I thought I would break out the 2016          
  edition of 13D and start reading, surely I would fall asleep            
quickly. I got to 6.5 Common Supply Pipes, 6.5.2 which            states; In 
common water supply connections servicing more            that one dwelling 
unit, 5 gpm shall be added to the            sprinkler system demand to 
determine the size of common            piping and the size of the total water 
supply            requirements...yada, yada, yada.            

            
            
So reading 6.5.2 I interpret that if it is a SFR (one              unit) I am 
not required to add 5 gpm domestic into the              calculations, correct?
            

            
            
Owen Evans
            

            
            

            
          
      
      
        
_______________________________________________
          Sprinklerforum mailing list
          [email protected]
          
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
        
      
      
      
      
      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

    
    
  

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to