Since its doesn’t fall under the definition of garages per 7.3.2 you are 
directed to 7.2. We had this situation a few months ago on a project and 
protected it per NFPA 13 OH 1 for parking garages.

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

 <mailto:[email protected]> [email protected]

 <http://www.norcalfire.com/> www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information 

belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Friday, August 25, 2017 3:30 AM
To: Sprinklerforum
Subject: Parking under 13R system

 

I am looking at a 3 story apartment building that is going to be protected by a 
13R system. Under one wing, the main level will be open for parking with 2 
floors of apartments above. 13R addresses garages but not open (on 2 sides) 
parking areas. A number of years ago, I did a similar arrangement, but it was a 
13 system and the space was protected by a dry system. Thought on if sprinklers 
are required?

 

I know there was a thread or 2 about this, but only found the one about 
sprinklers under train tracks. 


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-553-3553 (fax)

860-608-4559 (cell)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to