Rocco,
  

  
But could it fall under the definition of a carport and be excluded per 6.6.5?
  
  
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-553-3553 (tel:860-553-3553)  (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Aug 28, 2017 at 9:25 AM,  <Rocci Cetani 3 (mailto:[email protected])>  
> wrote:
>   
>   
>         
>   
>
>  Since its doesn’t fall under the definition of garages per 7.3.2 you are 
> directed to 7.2. We had this situation a few months ago on a project and 
> protected it per NFPA 13 OH 1 for parking garages.
>
>   
>
>     
>
>   
>   
>
>  Rocci Cetani III,    CET
>
>   
>
>  Senior Designer
>
>   
>
>  Water-Based Fire Protections Systems Layout, Nicet Level III
>
>   
>
>     
>
>   
>
>  Northern California Fire Protection Services Inc.
>
>   
>
>  16840 Joleen Way Bldg. A
>
>   
>
>  Morgan Hill, CA 93037
>
>   
>
>  P-(408) 776-1580 EXT.111
>
>   
>
>  F-(408) 776-1590
>
>   
>
>     
>
>   
>
>     
>
>   
>
>   [email protected] (mailto:[email protected])
>
>   
>
>   www.norcalfire.com (http://www.norcalfire.com/)
>
>   
>
>     
>
>   
>
>  CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
> contain confidential information     
>
>   
>
>  belonging to the sender. The information is intended only for the use of 
> individual or entity named above. If you are not the intended recipient, or 
> the employee or agent responsible to deliver this message to the intended 
> recipient, you are hereby notified that any disclosure, copying or taking of 
> any action in reliance on the contents of this information is strictly 
> prohibited. If you have received this transmission in error, please 
> immediately notify us by telephone to arrange for return of the documents.
>
>   
>   
>
>     
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  
> [email protected]
>   Sent:  Friday, August 25, 2017 3:30 AM
>   To:  Sprinklerforum
>   Subject:  Parking under 13R system
>
>   
>   
>   
>
>   
>
>   
>   
>
> I am looking at a 3 story apartment building that is going to be protected by 
> a 13R system. Under one wing, the main level will be open for parking with 2 
> floors of apartments above. 13R addresses garages but not open (on 2 sides) 
> parking areas. A number of years ago, I did a similar arrangement, but it was 
> a 13 system and the space was protected by a dry system. Thought on if 
> sprinklers are required?
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> I know there was a thread or 2 about this, but only found the one about 
> sprinklers under train tracks.   
>
>   
>   
>   
>   
>
>
>  Todd G Williams, PE
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
>   
>   
>   
>
> 860-553-3553 (tel:860-553-3553)  (fax)
>
>   
>   
>   
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>   
>   
>   
>   
>  _______________________________________________ Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   
  
  
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to