Negative. Check IBC for Grid Iron above stage. You need a compliment below it 
as well
R/
Matt

Sent from my Verizon 4G LTE Droid
On Oct 6, 2017 4:42 PM, "Reed A. Roisum, SET" <[email protected]> wrote:
I did take a look at the archives and found some information, but wondering 
about positioning of sprinklers above and below an “slatted” ceiling.  Not sure 
if that is the correct terminology.

It is above a stage where the rigging pulleys etc. are attached.  There are 
sprinklers at the deck which is probably 10’ above the slats.  The slats are 
between 3”-3 ½” wide (going off of photos) with approximately 1” – 1 /4” gap 
between.  They are about 1” – 1 ½” thick.  They look roughly 2 x 4 sized, but 
they are metal. There are no sprinklers located underneath the slats.  There 
are a few larger gaps to avoid other structural members etc. and then the cross 
supports underneath are probably 4” wide every 5’ or so.

Would this be considered an Open-Grid Ceiling from NFPA 13, 2013 ed. 8.15.14?  
A.8.15.14 says, “The installation of open-grid egg crate, louver, or honeycomb 
ceilings beneath sprinklers restricts the sideways travel of the sprinkler 
discharge and can change the character of the discharge.”  Is what I described 
more like a “louver” ceiling?

I know the gap is more than a ¼”.  We will say that the thickness does not 
exceed the least dimension of the opening (its close).  It’s tough to say 
whether it is 70% open or not??  In portions definitely not.

Question is, if I can meet all three of the above requirements then I do not 
need to install sprinklers under this slatted “ceiling”?  But if can’t meet one 
of the requirements then I do need sprinklers underneath?

Thank you for any insight.

Reed








Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to