Also, look at the IBC for stages and prosceniums. I believe that is where
you'll find Allen's standpipe requirement, among other whats and wheres.

On Sat, Oct 7, 2017 at 5:11 AM, Mark.Phelps <[email protected]> wrote:

> All good and true information Allen. I'm away from the "books" Right now
> but I believe a standpipe valve also needs to be installed at the stage
> area. Look up "Proscenium protection" in a word search in NFPA 13 and get
> the whole story.
>
> Mark at Aero
> 602 820-7894 <(602)%20820-7894>
>
> Sent from my iPhone
>
> On Oct 6, 2017, at 9:20 PM, AKS-Gmail-IMAP <[email protected]> wrote:
>
> Yes, and judging by the original question, you might be totally missing
> the boat as to what is needed and what goes on in what sounds like a full
> stage situation. Its the sprinklers underneath the grid iron that do the
> heavy lifting, not the sprinklers above the grid iron. The theater sets and
> curtains get pulled up to the grid iron, so you’ll need to find out how
> high they go and you’ll have to be comfortable with  whatever sprinkler
> spacing you come up with. It may be 6 or 8 feet from stage from to back.
> They’ll need guards, be multilevel and not be ordinary temperature. Beware
> the lights. Stages often get little AC or air movement because it can make
> noise and move the curtains. So up there at the grid iron and above is
> warmer than typical. There will probably be a catwalk level below the grid
> iron on the pulley side that requires sprinklers underneath it. There would
> also be an automatic smoke vent or two at the roof level that might have to
> be manually closed, which might mean some unlucky person has to do it from
> the grid iron level. You don’t want to have a part of the deck level
> sprinkler piping in the way making that task any more difficult than what
> it might be.
>
> Allan Seidel
> St. Louis, MO
>
> On Oct 6, 2017, at 5:57 PM, Matthew J Willis <[email protected]>
> wrote:
>
> Negative. Check IBC for Grid Iron above stage. You need a compliment below
> it as well
> R/ in the
> Matt
>
> *Sent from my Verizon 4G LTE Droid*
> On Oct 6, 2017 4:42 PM, "Reed A. Roisum, SET" <[email protected]>
> wrote:
>
> I did take a look at the archives and found some information, but
> wondering about positioning of sprinklers above and below an “slatted”
> ceiling.  Not sure if that is the correct terminology.
>
>
> It is above a stage where the rigging pulleys etc. are attached.  There
> are sprinklers at the deck which is probably 10’ above the slats.  The
> slats are between 3”-3 ½” wide (going off of photos) with approximately 1”
> – 1 /4” gap between.  They are about 1” – 1 ½” thick.  They look roughly 2
> x 4 sized, but they are metal. There are no sprinklers located underneath
> the slats.  There are a few larger gaps to avoid other structural members
> etc. and then the cross supports underneath are probably 4” wide every 5’
> or so.
>
>
> Would this be considered an Open-Grid Ceiling from NFPA 13, 2013 ed.
> 8.15.14?  A.8.15.14 says, *“The installation of open-grid egg crate,
> louver, or honeycomb ceilings beneath sprinklers restricts the sideways
> travel of the sprinkler discharge and can change the character of the
> discharge.”  *Is what I described more like a “louver” ceiling?
>
>
> I know the gap is more than a ¼”.  We will say that the thickness does not
> exceed the least dimension of the opening (its close).  It’s tough to say
> whether it is 70% open or not??  In portions definitely not.
>
>
> Question is, if I can meet all three of the above requirements then I do
> not need to install sprinklers under this slatted “ceiling”?  But if can’t
> meet one of the requirements then I do need sprinklers underneath?
>
>
> Thank you for any insight.
>
>
> Reed
>
>
>
>
>
>
>
>
> Reed A. Roisum, SET *|* *Karges-Faulconbridge, Inc.* *|* Senior Fire
> Protection Designer *|* Fargo, ND *| direct: *701.552.9903
> <(701)%20552-9903>* | **mobile:* 701.388.1352 <(701)%20388-1352> *| *
> *KFIengineers.com*
> <http://secure-web.cisco.com/1p70kFtdlqpHKox0rDKjW4_mNkaiyR4n8MZuMcs9hknsnmIZuakeQ5FGeSPSwfyJXWPf4ulR6mLm1vb-ikX50M4AfDH9ax9XPf80Ie2VeHtb_g623Wpg22HGGxFGAjmC1kEMqx5v-nnyiTqdKjSYohPGhhl6W6GSbVVbPaJt_xjhHNpfaVGLI40_yhnysJnGIRpe97pV9qUgt0hE49SPqCmtPrZH4d3vs-nG_18Jx1Xm-FnmGfAHgekLMK6_wVnxT/http%3A%2F%2Fwww.kfiengineers.com%2F>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://secure-web.cisco.com/1mZlXcSSesG869Y6_
> fosT8NF9PNPzazqHvuebse86flZgnjFY1U4pmH0LpUnDHYKZns9eoP_
> NPsKbaChNjJbwzzQjHzcB0ziip52oIQ8ZjfNvOaY8poYQY_3Dcb_omTHCxdHJbVV-
> WrCjBawqszktsAOogGBTl8CFphYSkGCcBejIgqENHQ_4lxt6hzMcGj7yRYuTW5-UQCq-
> vtIMc728bFotrPOR-DQdMaZWoPA_9OBLlf4-DpCdHALWc0CuGxNk/http%
> 3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-
> firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://secure-web.cisco.com/1mZlXcSSesG869Y6_
> fosT8NF9PNPzazqHvuebse86flZgnjFY1U4pmH0LpUnDHYKZns9eoP_
> NPsKbaChNjJbwzzQjHzcB0ziip52oIQ8ZjfNvOaY8poYQY_3Dcb_omTHCxdHJbVV-
> WrCjBawqszktsAOogGBTl8CFphYSkGCcBejIgqENHQ_4lxt6hzMcGj7yRYuTW5-UQCq-
> vtIMc728bFotrPOR-DQdMaZWoPA_9OBLlf4-DpCdHALWc0CuGxNk/http%
> 3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-
> firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>


-- 
Ron Greenman

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to