LH? We used number of heads. 20. At some older date we used 2” connection. Depending on layout the old and current are about equivalent.
Office system not designed with flex heads? Depends. Was there a huge buffer in original design? But if original had 1” sch 40 drops, that are changing to flex? Expect to provide them. When they created the generous coefficient for quick response and low ceilings, and combined with EC heads you could get down to six heads in offices. I remember calling the then incumbent NFPA staff P.E. for pamphlet 13. I asked about very minor T/I’s. The kind that were below our permit threshold, ‘field review, field inspect”. The answer I received was that all jobs in hydraulically designed systems require supporting calc’s. I felt it was more of a jD answer than a PE answer. Best Bruce Verhei > On Oct 6, 2017, at 13:59, rongreenman . <[email protected]> wrote: > > I think maybe large metropolitan areas have the resources to higher a higher > caliber of AHJ. Read that as better trained, more experienced, more educated > in code, what have you. Smaller jurisdictions have slackness, unhappy > firefighters drafted into the FMs office, or guys furiously trying to learn > who will Be subsequently courted by those jurisdictions with deeper pockets. > In the immediate Seattle area most AHJs are knowledgeable, fair and use good > judgement. Some are little Napoleons and others not really into their jobs > but these are rarer than in the areas further afield. A huge generalization > but I think for the most part true. > >> On Fri, Oct 6, 2017 at 1:19 PM Kyle.Montgomery <[email protected]> >> wrote: >> Travis, >> >> >> >> Are you seeing this in AZ, or are you doing a lot of work in other states? >> It seems like the AHJs we deal with in the valley are usually pretty lax on >> requiring calcs for T.I.s. >> >> >> >> -Kyle M >> >> >> >> From: Sprinklerforum [mailto:[email protected]] >> On Behalf Of Travis Mack >> Sent: Friday, October 06, 2017 6:16 AM >> To: [email protected] >> Subject: [EXTERNAL] Calcs and tenant improvements >> >> >> >> How many of you are being required to calculate systems when you do a tenant >> improvement? Just your run of the mill add/relocate. >> >> >> >> I am seeing it come up more and more. I am seeing it in situations where it >> is mostly relocates and no additions anywhere near the design areas. I have >> one now where the AHJ rejected for no calculations where the shell was OH2 >> and the new space is residential lofts. This particular AHJ wants us to show >> all piping on portions of the floor where no work is being done. They are >> also requiring us to submit plans for the two floors below our space that >> have no work being done. >> >> >> >> Is anyone else seeing stuff like this? >> >> >> >> Travis Mack, SET >> >> MFP Design, LLC >> >> "Follow" us on Facebook: >> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 >> >> Send large files to MFP Design via: >> >> https://www.hightail.com/u/MFPDesign >> >> >> >> Sent from my iPhone >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > -- > Sent from Gmail Mobile > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org