It is because of scenarios like these, the AHJ require calculations for
everything. It makes the ill informed/trained do what they should have done
originally.

 

Mike Hill

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Friday, October 06, 2017 10:22 AM
To: [email protected]
Subject: Re: Calcs and tenant improvements

 

This may not speak to your question in general terms, but has a third party
planner viewer for a local fire department I have kicked two tenant
improvements back and demanded couch recently.   one of them entailed the
Edition of 11 sprinklers in an area that already had 10, that was being
remodeled into small counseling cubicles. The end result was 21 sprinklers
in a space  no larger than 1200 square feet. The submitter put a note on the
plan saying that they were taking the exception of only counting sprinklers
in separate fire areas, his badly flawed premise being that the non-rated
walls forming the little rooms represented a fire area separation of sorts.

 

The other was a retail tenant Improvement in an existing Ordinary Hazard
shell building where outlets were spaced at 120 square feet and originally
designed for K5.6 sprinklers. The TI utilized extended coverage at 20 x 20.
The submitter's reasoning was it was like for like because the hazard didn't
change and there were fewer sprinklers.

 

Like everything else, we in the sprinkler community need to take ownership
of what is still a low standard of care in our industry. On the AHJ side of
the counter, we hope that common sense will prevail.

 

 

Steve

 

 

-------- Original message --------

From: Travis Mack <[email protected] <mailto:[email protected]> > 

Date: 10/6/17 6:39 AM (GMT-08:00) 

To: [email protected]
<mailto:[email protected]>  

Subject: Re: Calcs and tenant improvements 

 

Interesting to see what others run into. As far as the PE seal, that is
jurisdiction specific. We have PE on staff and seal in jurisdictions that
require. 

 

This has just been something that has been popping up more and more. It was
very rare in the past. We maybe calculated 1:100. Now I am seeing 3:5
requiring it for the jurisdictions I deal with. 

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone


On Oct 6, 2017, at 6:31 AM, [email protected]
<mailto:[email protected]>  wrote:

It depends on the jurisdiction, but I do see it. More of the rule and not
the exception. I don't see anything to the extreme you are talking about. 

 

I did have one recently where the existing sprinklers were installed on flex
drops and we have to move 5 sprinklers one pad over. The engineer stated if
we used flex drops (even the existing ones), the system had to calculated.
However, if we removed the flex and installed hard pipe, no calcs we're
required. 


Todd G Williams, PE 

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 <tel:860-535-2080>  (ofc)

860-553-3553 <tel:860-553-3553>  (fax)

860-608-4559 <tel:860-608-4559>  (cell)






On Oct 6, 2017 at 9:15 AM, <Travis Mack <mailto:[email protected]> >
wrote:

How many of you are being required to calculate systems when you do a tenant
improvement? Just your run of the mill add/relocate.  

 

I am seeing it come up more and more. I am seeing it in situations where it
is mostly relocates and no additions anywhere near the design areas. I have
one now where the AHJ rejected for no calculations where the shell was OH2
and the new space is residential lofts. This particular AHJ wants us to show
all piping on portions of the floor where no work is being done. They are
also requiring us to submit plans for the two floors below our space that
have no work being done. 

 

Is anyone else seeing stuff like this? 

 

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone

_______________________________________________ Sprinklerforum mailing list
[email protected]
<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to