While many of you may be thinking of (2013) NFPA 13 23.3.1 which is the general 
requirement for preparing hydraulic calculations...

I would like to remind the forum about 8.15.20.5 [Revamping of Hydraulic Design 
Systems] and more specifically 8.15.20.5.2 which states that "Calculations 
shall be provided to verify that the system design flow rate will be achieved." 
 If you have projects in jurisdictions enforcing an edition of NFPA 13 prior to 
2010, it may not be applied, since the 2010 edition is the one in which that 
specific requirement first appeared.  The variation of editions adopted in the 
many jurisdictions forum members have experienced may explain the variation in 
experiences of enforcement of this rule, in addition to the other "normal" 
factors that cause variation in enforcement...

Note that A.8.15.20.5.2 makes it clear that it is not the intent of the section 
to require a full hydraulic analysis of the existing piping system in addition 
to the new sprinkler layout.
In my experience, performing calculations in such scenarios can expose problems 
that should be made known.  It may bring to light deficiencies in the water 
supply [such as hydraulic degradation, increased hydraulic demand due to change 
of hazard, building owners who have not been paying for annual fire pump tests 
to be performed or do not address problems noted by the contractor on the 
report, etcetera].  The FAQ in the handbook is similar:  "When a hydraulically 
designed system is modified, new calculations must be provided to verify that 
the arrangement can provide the necessary flow and pressure.  The calculation 
must be made in the case of one or two sprinklers being supplied from the 
existing line fitting."

On the P.E. issue, our State's fire protection sprinkler systems law [Title 40, 
Chapter 10] requires the involvement of a P.E. on design of fire sprinkler 
systems, including additions and alterations, unless the building is exempted 
under the engineering law [Title 40, Chapter 22], such as when it is a one or 
two-family dwelling or a farm building not used for human occupancy, in which 
case a fire sprinkler contractor with a qualifier with the appropriate NICET IV 
certification is allowed to do the design in lieu of a P.E..

Please feel free to email me directly if you want more specifics about the 
sections, links to the laws, or have other questions for me.

Respectfully,

David Blackwell

David Blackwell, P.E.
Chief Engineer
(803)896-9833

Office of State Fire Marshal
141 Monticello Trail | Columbia, SC 29203
http://statefire.llr.sc.gov/
(803)896-9800

"Our firefighting starts with plan review..."

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Friday, October 06, 2017 11:36 AM
To: [email protected]
Subject: RE: Calcs and tenant improvements

*** SCDLLR NOTICE ***
*  This email is from an external email address. Please use caution when 
deciding whether to open any attachments or when clicking links.
*  Personally Identifiable Information (PII) should not be included in e-mail 
text or attachments. Do not save or transmit PII unencrypted.
I hear ya. My point is/was, while we may Know the system will work, others may 
not. Once the "core and shell" have been CO'd, subsequent modification become 
new work and subject to chapter 23, once again.
Each jurisdiction is of course different. For instance, I have never seen a 
safety factor for "future tenants". Only for field changes during current 
review/build/install.

Getting the water flow information, and having to survey back to the System 
Riser are the main problems for this, without a doubt.

R/
Matt

"As-Built", adjective.

  *   "  A mythological creation of the Fire Sprinkler Industry meant to result 
in dazed and confused looks when requested."



Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:[email protected]]



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Michael Hill
Sent: Friday, October 6, 2017 8:58 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Calcs and tenant improvements

As I am sure you are aware, many jurisdictions adopt/modify the standards and 
seem to apply them differently. Most jurisdictions we work in require 
substantial safety factors when calculating base building sprinkler 
installations. The reasons given for these are usually "to allow field changes" 
and to "account for future tenant revisions". For instance, you would only be 
required to calculate the most demanding area of the highest typical floor in a 
multi-story office building. Any tenants on lower levels that matched the 
original pipe sizing and spacing would not require new hydraulic calculations. 
That has gone away for many jurisdictions, as they now require new calculations 
on all tenant improvements.

On the flip side of this. I have been asked to calculate projects that I would 
have argued did not need them, as I was matching existing conditions that had 
already been proven by hydraulic calculations, only to find these areas to be 
more demanding.

I do not mind having to do calculations on every project. We are however, 
finding it difficult to obtain water flow information in a timely manner from 
several local jurisdictions.

Mike Hill

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Friday, October 06, 2017 10:41 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Calcs and tenant improvements

It's Friday so..,

Where does it say in 13 that you do Not provided calcs?

If I read 23.1.3 they are required no?

R/
Matt



Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:[email protected]]



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Michael Hill
Sent: Friday, October 6, 2017 8:28 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Calcs and tenant improvements

It is because of scenarios like these, the AHJ require calculations for 
everything. It makes the ill informed/trained do what they should have done 
originally.

Mike Hill

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Friday, October 06, 2017 10:22 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Calcs and tenant improvements

This may not speak to your question in general terms, but has a third party 
planner viewer for a local fire department I have kicked two tenant 
improvements back and demanded couch recently.   one of them entailed the 
Edition of 11 sprinklers in an area that already had 10, that was being 
remodeled into small counseling cubicles. The end result was 21 sprinklers in a 
space  no larger than 1200 square feet. The submitter put a note on the plan 
saying that they were taking the exception of only counting sprinklers in 
separate fire areas, his badly flawed premise being that the non-rated walls 
forming the little rooms represented a fire area separation of sorts.

The other was a retail tenant Improvement in an existing Ordinary Hazard shell 
building where outlets were spaced at 120 square feet and originally designed 
for K5.6 sprinklers. The TI utilized extended coverage at 20 x 20. The 
submitter's reasoning was it was like for like because the hazard didn't change 
and there were fewer sprinklers.

Like everything else, we in the sprinkler community need to take ownership of 
what is still a low standard of care in our industry. On the AHJ side of the 
counter, we hope that common sense will prevail.


Steve


-------- Original message --------
From: Travis Mack <[email protected]<mailto:[email protected]>>
Date: 10/6/17 6:39 AM (GMT-08:00)
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Calcs and tenant improvements

Interesting to see what others run into. As far as the PE seal, that is 
jurisdiction specific. We have PE on staff and seal in jurisdictions that 
require.

This has just been something that has been popping up more and more. It was 
very rare in the past. We maybe calculated 1:100. Now I am seeing 3:5 requiring 
it for the jurisdictions I deal with.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Oct 6, 2017, at 6:31 AM, [email protected]<mailto:[email protected]> 
wrote:
It depends on the jurisdiction, but I do see it. More of the rule and not the 
exception. I don't see anything to the extreme you are talking about.

I did have one recently where the existing sprinklers were installed on flex 
drops and we have to move 5 sprinklers one pad over. The engineer stated if we 
used flex drops (even the existing ones), the system had to calculated. 
However, if we removed the flex and installed hard pipe, no calcs we're 
required.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-553-3553<tel:860-553-3553> (fax)
860-608-4559<tel:860-608-4559> (cell)

On Oct 6, 2017 at 9:15 AM, <Travis Mack<mailto:[email protected]>> wrote:
How many of you are being required to calculate systems when you do a tenant 
improvement? Just your run of the mill add/relocate.

I am seeing it come up more and more. I am seeing it in situations where it is 
mostly relocates and no additions anywhere near the design areas. I have one 
now where the AHJ rejected for no calculations where the shell was OH2 and the 
new space is residential lofts. This particular AHJ wants us to show all piping 
on portions of the floor where no work is being done. They are also requiring 
us to submit plans for the two floors below our space that have no work being 
done.

Is anyone else seeing stuff like this?

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone
_______________________________________________ Sprinklerforum mailing list 
[email protected]<mailto:[email protected]>
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to