I think that is a pretty solid assumption. I just had a seminar about attic 
sprinklers and that is exactly what happened in the tests they showed.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark Sornsin [FAR]
Sent: Wednesday, October 11, 2017 6:49 AM
To: '[email protected]' 
<[email protected]>
Subject: [EXTERNAL] RE: Attic Design, Using BB1 & AP Sprinklers

Not sure I agree with this, Tony.  I don’t recall the design guidelines 
requiring the second calc flowing a bunch of sprinklers at the eave.

If I had to guess I would say we don’t see that calc called out because an 
attic fire tends to not spread along the eave. Rather if it starts there it 
quickly moves up the slope towards the ridgeline, with limited horizontal 
spread.  I would assume that testing shows no more than two sprinklers operate 
at the eave with 3 or 4 typically operating at the peak – or something similar. 
Thus the recommended design with some safety factor calls out 7 at the peak and 
two at the eave. But this is just my knee-jerk assumption.

-Mark


[Visit our Website at 
http://secure-web.cisco.com/1AT5Ul-WsOAbqZwoIttKNr26lYL4B9PuvaLq-6t_OhZWrLQn-R3i3Vn5hc1VrTrSc5RiFlDuTM_VRqgP4fCDzL46pLDJOBs4gRMMrs_vsDdCV27PyrS_2b1jqwzyTM-Wqe6RofDRrdkNGFotuMRnt9vwj9w5vGYJ_JkPlHSDwy2WieBcWq3BvpE02Cm-kvz7r2OATr-NrXjroUmrejhdKvHlTMQojC8HZD4j456822kl634XhKH0HD4R21hMP0D-b7gQCMXYHJrp2W_E_r7kKSg/http%3A%2F%2Fwww.SummitCoUS.com]<http://secure-web.cisco.com/1AT5Ul-WsOAbqZwoIttKNr26lYL4B9PuvaLq-6t_OhZWrLQn-R3i3Vn5hc1VrTrSc5RiFlDuTM_VRqgP4fCDzL46pLDJOBs4gRMMrs_vsDdCV27PyrS_2b1jqwzyTM-Wqe6RofDRrdkNGFotuMRnt9vwj9w5vGYJ_JkPlHSDwy2WieBcWq3BvpE02Cm-kvz7r2OATr-NrXjroUmrejhdKvHlTMQojC8HZD4j456822kl634XhKH0HD4R21hMP0D-b7gQCMXYHJrp2W_E_r7kKSg/http%3A%2F%2Fwww.SummitCoUS.com>

Mark Sornsin
Sr. Fire Protection Engineer
Direct: 701-499-1391
Cell: 701-526-8585


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tony Silva
Sent: Tuesday, October 10, 2017 4:40 PM
To: [email protected]<mailto:[email protected]>; 
[email protected]<mailto:[email protected]>
Subject: Re: Attic Design, Using BB1 & AP Sprinklers

You need 2 calcs. One is the 7 BB + 2 AP's. The second calc is only AP heads. 
The length of the design area will be based on the 1950 sf design area, so you 
will need to calc more than 2 AP heads. At least that is how I would do it.
Tony

On Tue, Oct 10, 2017 at 2:33 PM, Joseph Meyer 
<[email protected]<mailto:[email protected]>> wrote:

Assisted living facility under NFPA 13 with an attic above entry level with a 
42 foot wide span. We are able to use BB1 sprinklers along the attic ridge 
line, but the main size becomes slightly inflated when designed this way.

Tyco's published literature regarding attic sprinklers indicate that BB1 
sprinklers along the ridge, used with AP sprinklers at the eaves on a dry 
system should be calculated using seven BB sprinklers plus up to two most 
demanding AP sprinklers (Figure 20-B-2 from TFP610 page 20, below).

If the AP sprinklers at the eaves are on their own branch lines running 
perpendicular to structure (see Figure 14A below), should these branch lines 
really be sized to only accommodate two sprinklers? Figure 20-C-3 indicates 
that AP sprinklers should be calculated using the most demanding 1950 sqft, but 
this appears to describe hip roofs, not a traditional gable. Any insight is 
appreciated, thanks in advance.



[cid:[email protected]]

[cid:[email protected]]




--


Joe Meyer, P.E.
Fire Protection Engineer
[SSC          Engineering]
18207 Edison Avenue
Chesterfield, MO 63005
Office Phone: (636) 530-7770<tel:(636)%20530-7770>
Fax: (636) 530-7877<tel:(636)%20530-7877>
[email protected]<mailto:[email protected]>

Fire Alarm | Fire Suppression | Life Safety

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://secure-web.cisco.com/1z0QekKIeCwXSsXp7pqBVwKYWlxLeJlSYmaD_V6jk3GLr2V6gJHKnqva7YN2O8abDzmna0xT-gUDZ3TlrPB0vub90rCHOWyot09mM7hjuatQit_KfUovGMDAjDn8wtYyaJos1q9TCk72oAmup8eDeu9IUB1SbgtTK-0aKnhpVPR9lH3e9Z_WcykWzjZOf-U5Wh3PsCKmGEVKv4EXzZPInQWziLenVzG2c04bzg_jIoG4891rpym3yeaeqdSzNymYNFrkb6GmWKZprBoRri2ZwAQ/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to