Can you draft the question and get the AHJ to submit it? 

NFPA does seem to reply much quicker to AHJ’s. 

Include a section. A simple sketch can sometimes prevent a lot of 
misunderstanding. 

And just the facts.

Best

Bruce Verhei 


> On Oct 20, 2017, at 13:47, Jerry Van Kolken <[email protected]> wrote:
> 
> Mr. Leyton,
> Do you know where I can find that amendment for California? And when it went 
> into effect?
> 
> Jerry Van Kolken
> Millennium Fire Protection
> (760) 722-2722
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Steve Leyton
> Sent: Tuesday, November 10, 2015 4:33 PM
> To: [email protected]
> Subject: RE: Quick Response Reduction
> 
> 
> 
> Mr. Bilbo:
> Our esteemed State Building Standards Commission has amended NFPA 13 to 
> exclude the quick response area reduction for ordinary hazard. We also have 
> an amendment that when a reduction is taken, the design area shall be 7 
> sprinklers minimum and not 5.
> Sincerely and spologetically,California 
> 
> -------- Original message --------
> From: Sprinkler Academy - C Bilbo <[email protected]>
> Date: 11/10/2015  4:30 PM  (GMT-08:00)
> To: [email protected]
> Subject: RE: Quick Response Reduction 
> 
> Mr Stites,
> 
> You may care to review the four requirements for using the Quick Response 
> Reduction (Is that 11.2.3.2.3?) One of the "Design Advantage" strategies is 
> to use the QR Redux in Ordinary Hazard and this can significantly affect the 
> cost of a system. Yo.
> 
> It should be recognized that the above is my opinion as a member of the NFPA, 
> and has not been processed as a formal interpretation in accordance with the 
> NFPA Regulations Governing Committee Projects and should therefore not be 
> considered, nor relied upon, as the official position of the the NFPA, nor 
> any of their technical committees. 
> 
> Sincerely,
> 
> 
> Cecil Bilbo
> Academy of Fire Sprinkler Technology
> Champaign, IL
> 217.607.0325
> www.sprinkleracademy.com
> 
> [email protected]
> 
> 
> 
> OUR STUDENTS SAVE LIVES!!
> 
> 
> 
>> From: [email protected]
>> Date: Tue, 10 Nov 2015 15:15:10 -0800
>> Subject: Re: Quick Response Reduction
>> To: [email protected]
>> 
>> Also, just a "heads-up" but in California you can only take that 
>> reduction for Light Hazard...is that what he's thinking possibly?
>> 
>> Gary
>> 
>> On Tue, Nov 10, 2015 at 2:04 PM, Roland Huggins 
>> <[email protected]>
>> wrote:
>> 
>>> with the understanding that it is available only if you are an NFPA 
>>> member
>>> - just like AFSA informal interpretations.
>>> 
>>> Roland
>>> 
>>> 
>>> Roland Huggins, PE - VP Engineering
>>> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves 
>>> Lives Dallas, TX http://www.firesprinkler.org 
>>> <http://www.firesprinkler.org/>
>>> 
>>> 
>>> 
>>> 
>>> 
>>>> On Nov 10, 2015, at 1:11 PM, [email protected] wrote:
>>>> 
>>>> Regarding AHJ code interpretation issues, my experience is that an
>>> informal interpretation from NFPA will resolve almost all issues. 
>>> They can be obtained fairly quickly by contacting NFPA. The only 
>>> exception would be where the local AHJ has specific requirements over and 
>>> above NFPA code.
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> Bill Menster
>>>> WFM Consulting Inc.
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>>> 
>> 
>> 
>> 
>> --
>> Gary Stites
>> *805-769-GMAN*
>> 
>> RLH <http://www.rlhfp.com>
>> WWW.K25.Rocks
>> Pandora Station <http://www.pandora.com/?sc=sh43464983213902734>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>                         
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org